Basic site-to-site VPN with digital certificate

Basic site-to-site VPN with digital certificate

This is a sample configuration of IPsec VPN authenticating a remote FortiGate peer with a certificate. The certificate on one peer is validated by the presence of the CA certificate that is installed on the other peer.

The VPN Wizard is used to configure a site-to-site VPN tunnel.

It is assumed that the certificates have been configured and imported to the FortiGates. For information about configuring certificates using third party tools, such as XCA, see Creating certificates with XCA. For information about importing a certificate, see Import a certificate.

Individual settings can vary, but in order for the tunnel to come up, the configuration must be the same on both FortiGates.

For more information on IPsec settings, see Phase 1 configuration and Phase 2 configuration.

To configure an IPsec VPN using the VPN Wizard on the HQ1 FortiGate:
  1. Go to VPN > VPN Wizard.

  2. Enter a name for the VPN in the Tunnel name field. In this example, HQ2B2

  3. Set Select a template to Site to Site.

  4. Click Begin.

  5. Configure the VPN tunnel settings:

    Field

    Value

    Authentication method

    Signature

    Certificate name

    Select a certificate.

    Peer certificate CA

    Select a peer CA certificate.

    IKE

    Version 2

    Transport

    Auto

    Leave Use Fortinet encapsulation toggled off.

    NAT traversal

    Enable

    Set Keepalive frequency to 10.

  6. Click Next.

  7. Configure the Remote site settings:

    Field

    Value

    Remote site device type

    FortiGate

    Remote site device

    Accessible and static

    Set IP/FQDN to 10.100.68.5.

    Route this device's internet traffic through the remote site.

    Disabled

    Remote site subnets that can access VPN

    10.2.0.0/24

  8. Click Next.

  9. Configure the Local site settings:

    Field

    Value

    Outgoing interface that binds to tunnel

    port1 (the WAN interface in this example)

    Disable Create and add interface to zone if you do not need a zone to be created.

    Local interface

    port2 (in this example)

    Local subnets that can access VPN

    This field automatically uses the IP address related to the selected local interface. In this example, 10.100.77.0/24

    Allow remote site's internet traffic through this device

    Disabled

  10. Click Next.

  11. Review the configuration and, if everything is correct, click Submit.

To configure an IPsec VPN using the VPN Wizard on the HQ2 FortiGate:
  1. Go to VPN > VPN Wizard.

  2. Enter a name for the VPN in the Tunnel name field. In this example, B2toHQ

  3. Set Select a template to Site to Site.

  4. Click Begin.

  5. Configure the VPN tunnel settings:

    Field

    Value

    Authentication method

    Signature

    Certificate name

    Select a certificate.

    Peer certificate CA

    Select a peer CA certificate.

    IKE

    Version 2

    Transport

    Auto

    Leave Use Fortinet encapsulation toggled off.

    NAT traversal

    Enable

    Set Keepalive frequency to 10.

  6. Click Next.

  7. Configure the Remote site settings:

    Field

    Value

    Remote site device type

    FortiGate

    Remote site device

    Accessible and static

    Set IP/FQDN to 10.100.64.101.

    Route this device's internet traffic through the remote site.

    Disabled

    Remote site subnets that can access VPN

    10.100.77.0/24

  8. Click Next.

  9. Configure the Local site settings:

    Field

    Value

    Outgoing interface that binds to tunnel

    port1 (the WAN interface in this example)

    Enable Create and add interface to zone.

    Local interface

    port3 (in this example)

    Local subnets that can access VPN

    This field automatically uses the IP address related to the selected local interface. In this example, 10.2.0.0/24

    Allow remote site's internet traffic through this device

    Disabled

  10. Click Next.

  11. Review the configuration and, if everything is correct, click Submit.

To configure HQ1 for IPsec VPN authenticating a remote FortiGate peer with a digital certificate using the CLI:
  1. Configure the WAN interface and default route.

    The WAN interface is the interface connected to the ISP. The IPsec tunnel is established over the WAN interface.

    config system interface 
        edit "port1"
            set vdom "root"
            set ip 10.100.64.101 255.255.255.0
        next
    end
    config router static
        edit 1
            set gateway 10.100.64.102
            set device "port1"
        next
    end
  2. Configure address objects for internal protected networks.

    config firewall address
        edit "10.2.0.0"
            set subnet 10.2.0.0 255.255.255.0
        next
        edit "10.100.77.0"
            set subnet 10.100.77.0 255.255.255.0
        next
    end
  3. Configure the internal (protected subnet) interface.

    The internal interface connects to the corporate internal network. Traffic from this interface routes out the IPsec VPN tunnel.

    config system interface
        edit "port2"
            set vdom "root"
            set ip 10.100.77.0 255.255.255.0
        next
    end
  4. Configure the import certificate and its CA certificate information.

    The certificate and its CA certificate must be imported on the remote peer FortiGate and on the primary FortiGate before configuring IPsec VPN tunnels. If the built-in Fortinet_Factory certificate and the Fortinet_CA CA certificate are used for authentication, you can skip this step.

    config vpn certificate local
        edit "test1"
            ...
            set range global
        next
    end
    config vpn certificate ca
        edit "CA_Cert_1"
            ...
            set range global
        next
    end
  5. Configure the peer user.

    The peer user is used in the IPsec VPN tunnel peer setting to authenticate the remote peer FortiGate.

    • If not using the built-in Fortinet_Factory certificate and Fortinet_CA CA certificate:

      config user peer
          edit "peer1"
              set ca "CA_Cert_1"
          next
      end
    • If the built-in Fortinet_Factory certificate and Fortinet_CA CA certificate are used for authentication, the peer user must be configured based on Fortinet_CA:

      config user peer
          edit "peer1"
              set ca "Fortinet_CA"
          next
      end
  6. Configure the IPsec phase1-interface.

    config vpn ipsec phase1-interface
        edit "HQ2B2"
            set interface "port1"
            set ike-version 2
            set authmethod signature
            set net-device enable
            set proposal aes128-sha256 aes256-sha256 aes128-sha1 aes256-sha1
            set remote-gw 10.100.68.5
            set certificate "test1"
            set peer "peer1"
        next
    end
  7. Configure the IPsec phase2-interface.

    config vpn ipsec phase2-interface
        edit "HQ2B2"
            set phase1name "HQ2B2 "
            set proposal aes128-sha1 aes256-sha1 aes128-sha256 aes256-sha256 aes128gcm aes256gcm chacha20poly1305
            set auto-negotiate enable
            set src-addr-type name
            set dst-addr-type name
            set src-name "10.100.77.0"
            set dst-name "10.2.0.0"
        next
    end
  8. Configure the static routes.

    Two static routes are added to reach the remote protected subnet. The blackhole route is important to ensure that IPsec traffic does not match the default route when the IPsec tunnel is down.

    config router static
        edit 2
            set dst 10.20.0.0 255.255.255.0
            set device "HQ2B2"
        next
        edit 3
            set dst 10.20.0.0 255.255.255.0
            set blackhole enable
            set distance 254
        next
    end
  9. Configure two firewall policies to allow bidirectional IPsec traffic flow over the IPsec VPN tunnel.

    config firewall policy
        edit 1
            set name "inbound"
            set srcintf "HQ2B2"
            set dstintf "port2"
            set srcaddr "10.2.0.0"
            set dstaddr "10.100.77.0"
            set action accept
            set schedule "always"
            set service "ALL"
        next
        edit 2
            set name "outbound"
            set srcintf "port2"
            set dstintf "HQ2B2"
            set srcaddr "10.100.77.0"
            set dstaddr "10.2.0.0"
            set action accept
            set schedule "always"
            set service "ALL"
        next
    end
To configure HQ2 for IPsec VPN authenticating a remote FortiGate peer with a digital certificate using the CLI:
  1. Configure the WAN interface and default route.

    config system interface 
        edit "port1"
            set vdom "root"
            set ip 10.100.68.5 255.255.255.0
        next
    end
    config router static
        edit 1
            set gateway 10.100.68.2
            set device "port1"
        next
    end
  2. Configure address objects for internal protected networks.

    config firewall address
        edit "10.2.0.0"
            set subnet 10.2.0.0 255.255.255.0
        next
    end
    config firewall address
        edit "10.100.77.0"
            set subnet 10.100.77.0 255.255.255.0
        next
    end
  3. Configure the internal (protected subnet) interface.

    config system interface
        edit "port3"
            set vdom "root"
            set ip 10.2.0.0 255.255.255.0
        next
    end
  4. Configure the import certificate and its CA certificate information.

    config vpn certificate local
        edit "test2"
            ...
            set range global
        next
    end
    config vpn certificate ca
        edit "CA_Cert_1"
            ...
            set range global
        next
    end
  5. Configure the peer user.

    • If not using the built-in Fortinet_Factory certificate and Fortinet_CA CA certificate:

      config user peer
          edit "peer2"
              set ca "CA_Cert_1"
          next
      end
    • If the built-in Fortinet_Factory certificate and Fortinet_CA CA certificate are used for authentication, the peer user must be configured based on Fortinet_CA:

      config user peer
          edit "peer2"
              set ca "Fortinet_CA"
          next
      end
  6. Configure the IPsec phase1-interface.

    config vpn ipsec phase1-interface
        edit "HQ2B2"
            set interface "port1"
            set ike-version 2
            set authmethod signature
            set net-device enable
            set proposal aes128-sha256 aes256-sha256 aes128-sha1 aes256-sha1
            set remote-gw 10.100.68.5
            set certificate "test1"
            set peer "peer1"
        next
    end
  7. Configure the IPsec phase2-interface.

    config vpn ipsec phase2-interface
        edit "B2toHQ"
            set phase1name "B2toHQ"
            set proposal aes128-sha1 aes256-sha1 aes128-sha256 aes256-sha256 aes128gcm aes256gcm chacha20poly1305
            set auto-negotiate enable
            set src-addr-type name
            set dst-addr-type name
            set src-name "10.2.0.0"
            set dst-name "10.100.77.0"
        next
    end
  8. Configure the static routes.

    config router static
        edit 2
            set dst 10.100.77.0 255.255.255.0
            set device "B2toHQ"
        next
        edit 3
            set dst 10.100.77.0 255.255.255.0
            set blackhole enable
            set distance 254
        next
    end
  9. Configure two firewall policies to allow bidirectional IPsec traffic flow over the IPsec VPN tunnel.

    config firewall policy
        edit 1
            set name "inbound"
            set srcintf "B2toHQ"
            set dstintf "port3"
            set srcaddr "10.100.77.0"
            set dstaddr "10.2.0.0"
            set action accept
            set schedule "always"
            set service "ALL"
        next
        edit 2
            set name "outbound"
            set srcintf "port3"
            set dstintf "B2toHQ"
            set srcaddr "10.2.0.0"
            set dstaddr "10.100.77.0"
            set action accept
            set schedule "always"
            set service "ALL"
        next
    end
To verify the tunnel status in the GUI:
  1. On FortiGate HQ1, go to Dashboard > Network and expand the IPsec widget.

  2. Find the new tunnel, HQ2B2 in this example, and check that both Phase 1 and Phase 2 Tunnel are up.

  3. Verify the tunnel status on HQ2 in the same way.

To verify the tunnel status in the CLI:
  1. On FortiGate HQ1, run the following command:

    # diagnose vpn ike gateway list name HQ2B2
    vd: root/0
    name: HQ2B2
    version: 2
    interface: port1 3
    addr: 10.100.64.101:500 -> 10.100.68.5:500
    tun_id: 10.100.68.5/::10.100.68.5
    remote_location: 0.0.0.0
    network-id: 0
    transport: UDP
    created: 852804s ago
    peer-id: 10.100.68.5
    peer-id-auth: no
    pending-queue: 0
    PPK: no
    IKE SA: created 1/11  established 1/11  time 0/820/9010 ms
    IPsec SA: created 1/21  established 1/21  time 0/433/9010 ms
    
    id/spi: 8895 45e69522bd784183/69be2940ae314677
    direction: responder
    status: established 77898-77898s ago = 0ms
    proposal: aes128-sha256
    child: yes
    SK_ei: 07446ef38bd406fa-18e45bec886a2bd3
    SK_er: b940f4338b27f369-7beaa308b7241a1b
    SK_ai: 61eeb720d062c70b-e606340beab6f9d5-3a4da2966373ab15-e5766540cf6c7dd1
    SK_ar: bbdd888b98dbda7b-669da7a726ce2148-3f08940f802f580c-52b6ef93f48672aa
    message-id sent/recv: 0/1783
    QKD: no
    lifetime/rekey: 86400/8231
    DPD sent/recv: 00000000/00000000
    peer-id: 10.100.68.5

    Note that HQ1 acted as the responder, and established the tunnel with remote peer 10.100.68.5 over UDP/500.

  2. On FortiGate HQ2, run the following command:

    # diagnose vpn ike gateway list name B2toHQ 
    vd: root/0
    name: B2toHQ
    version: 2
    interface: port1 3
    addr: 10.100.68.5:500 -> 10.100.64.101:500
    tun_id: 10.100.64.101/::10.100.64.101
    remote_location: 0.0.0.0
    network-id: 0
    transport: UDP
    created: 853181s ago
    peer-id: 10.100.64.101
    peer-id-auth: no
    pending-queue: 0
    PPK: no
    IKE SA: created 1/11  established 1/11  time 0/5/10 ms
    IPsec SA: created 1/21  established 1/21  time 0/0/10 ms
    
    id/spi: 5788 45e69522bd784183/69be2940ae314677
    direction: initiator
    status: established 78281-78281s ago = 10ms
    proposal: aes128-sha256
    child: yes
    SK_ei: 07446ef38bd406fa-18e45bec886a2bd3
    SK_er: b940f4338b27f369-7beaa308b7241a1b
    SK_ai: 61eeb720d062c70b-e606340beab6f9d5-3a4da2966373ab15-e5766540cf6c7dd1
    SK_ar: bbdd888b98dbda7b-669da7a726ce2148-3f08940f802f580c-52b6ef93f48672aa
    message-id sent/recv: 1792/0
    QKD: no
    lifetime/rekey: 86400/7818
    DPD sent/recv: 00001ed7/00001ed7
    peer-id: 10.100.64.101

    Note that HQ2 acted as the initiator, and established the tunnel with remote peer 10.100.64.101 over UDP/500.

To verify traffic through the IPsec tunnel:
  1. On a PC connected behind the port2 interface of HQ1, initiate ICMP traffic to the 10.2.0.0/24 network and verify that traffic goes through:

    root@dmz-public-server:~# ping 10.2.0.7
    PING 10.2.0.7 (10.2.0.7) 56(84) bytes of data.
    64 bytes from 10.2.0.7: icmp_seq=1 ttl=62 time=9.84 ms
    64 bytes from 10.2.0.7: icmp_seq=2 ttl=62 time=0.808 ms
    
  2. Verify the traffic on HQ1:

    # diagnose sniffer packet any 'host 10.2.0.7' 4 0 l
    Using Original Sniffing Mode
    interfaces=[any]
    filters=[host 10.2.0.7]
    2024-11-05 12:06:05.509027 port2 in 10.100.77.101 -> 10.2.0.7: icmp: echo request
    2024-11-05 12:06:05.509074 HQ2B2 out 10.100.77.101 -> 10.2.0.7: icmp: echo request
    2024-11-05 12:06:05.518607 HQ2B2 in 10.2.0.7 -> 10.100.77.101: icmp: echo reply
    2024-11-05 12:06:05.518632 port2 out 10.2.0.7 -> 10.100.77.101: icmp: echo reply
    

    The ICMP request packets are received on port2 and routed to the HQ2B2 tunnel. ICMP reply packets are received on the HQ2B2 tunnel and routed back out port2.

  3. Verify the traffic on HQ12:

    # diagnose sniffer packet any 'host 10.100.77.101' 4 0 l
    Using Original Sniffing Mode
    interfaces=[any]
    filters=[host 10.100.77.101]
    2024-11-05 12:06:05.509711 B2toHQ in 10.100.77.101 -> 10.2.0.7: icmp: echo request
    2024-11-05 12:06:05.509791 port3 out 10.100.77.101 -> 10.2.0.7: icmp: echo request
    2024-11-05 12:06:05.518809 port3 in 10.2.0.7 -> 10.100.77.101: icmp: echo reply
    2024-11-05 12:06:05.518899 B2toHQ out 10.2.0.7 -> 10.100.77.101: icmp: echo reply 
    

    The ICMP request is received on the B2toHQ tunnel and routed to port3. The ICMP reply is received on port3 and routed back out the B2toHQ.

  4. Optionally, run real time IKE debug using appropriate filters for troubleshooting if the IPsec tunnel does not come up:

    diagnose debug application ike -1

    If the remote FortiGate certificate cannot be validated, the following error is shown in the debug output:

    ike 0: to_HQ2:15314: certificate validation failed

Basic site-to-site VPN with digital certificate

Basic site-to-site VPN with digital certificate

This is a sample configuration of IPsec VPN authenticating a remote FortiGate peer with a certificate. The certificate on one peer is validated by the presence of the CA certificate that is installed on the other peer.

The VPN Wizard is used to configure a site-to-site VPN tunnel.

It is assumed that the certificates have been configured and imported to the FortiGates. For information about configuring certificates using third party tools, such as XCA, see Creating certificates with XCA. For information about importing a certificate, see Import a certificate.

Individual settings can vary, but in order for the tunnel to come up, the configuration must be the same on both FortiGates.

For more information on IPsec settings, see Phase 1 configuration and Phase 2 configuration.

To configure an IPsec VPN using the VPN Wizard on the HQ1 FortiGate:
  1. Go to VPN > VPN Wizard.

  2. Enter a name for the VPN in the Tunnel name field. In this example, HQ2B2

  3. Set Select a template to Site to Site.

  4. Click Begin.

  5. Configure the VPN tunnel settings:

    Field

    Value

    Authentication method

    Signature

    Certificate name

    Select a certificate.

    Peer certificate CA

    Select a peer CA certificate.

    IKE

    Version 2

    Transport

    Auto

    Leave Use Fortinet encapsulation toggled off.

    NAT traversal

    Enable

    Set Keepalive frequency to 10.

  6. Click Next.

  7. Configure the Remote site settings:

    Field

    Value

    Remote site device type

    FortiGate

    Remote site device

    Accessible and static

    Set IP/FQDN to 10.100.68.5.

    Route this device's internet traffic through the remote site.

    Disabled

    Remote site subnets that can access VPN

    10.2.0.0/24

  8. Click Next.

  9. Configure the Local site settings:

    Field

    Value

    Outgoing interface that binds to tunnel

    port1 (the WAN interface in this example)

    Disable Create and add interface to zone if you do not need a zone to be created.

    Local interface

    port2 (in this example)

    Local subnets that can access VPN

    This field automatically uses the IP address related to the selected local interface. In this example, 10.100.77.0/24

    Allow remote site's internet traffic through this device

    Disabled

  10. Click Next.

  11. Review the configuration and, if everything is correct, click Submit.

To configure an IPsec VPN using the VPN Wizard on the HQ2 FortiGate:
  1. Go to VPN > VPN Wizard.

  2. Enter a name for the VPN in the Tunnel name field. In this example, B2toHQ

  3. Set Select a template to Site to Site.

  4. Click Begin.

  5. Configure the VPN tunnel settings:

    Field

    Value

    Authentication method

    Signature

    Certificate name

    Select a certificate.

    Peer certificate CA

    Select a peer CA certificate.

    IKE

    Version 2

    Transport

    Auto

    Leave Use Fortinet encapsulation toggled off.

    NAT traversal

    Enable

    Set Keepalive frequency to 10.

  6. Click Next.

  7. Configure the Remote site settings:

    Field

    Value

    Remote site device type

    FortiGate

    Remote site device

    Accessible and static

    Set IP/FQDN to 10.100.64.101.

    Route this device's internet traffic through the remote site.

    Disabled

    Remote site subnets that can access VPN

    10.100.77.0/24

  8. Click Next.

  9. Configure the Local site settings:

    Field

    Value

    Outgoing interface that binds to tunnel

    port1 (the WAN interface in this example)

    Enable Create and add interface to zone.

    Local interface

    port3 (in this example)

    Local subnets that can access VPN

    This field automatically uses the IP address related to the selected local interface. In this example, 10.2.0.0/24

    Allow remote site's internet traffic through this device

    Disabled

  10. Click Next.

  11. Review the configuration and, if everything is correct, click Submit.

To configure HQ1 for IPsec VPN authenticating a remote FortiGate peer with a digital certificate using the CLI:
  1. Configure the WAN interface and default route.

    The WAN interface is the interface connected to the ISP. The IPsec tunnel is established over the WAN interface.

    config system interface 
        edit "port1"
            set vdom "root"
            set ip 10.100.64.101 255.255.255.0
        next
    end
    config router static
        edit 1
            set gateway 10.100.64.102
            set device "port1"
        next
    end
  2. Configure address objects for internal protected networks.

    config firewall address
        edit "10.2.0.0"
            set subnet 10.2.0.0 255.255.255.0
        next
        edit "10.100.77.0"
            set subnet 10.100.77.0 255.255.255.0
        next
    end
  3. Configure the internal (protected subnet) interface.

    The internal interface connects to the corporate internal network. Traffic from this interface routes out the IPsec VPN tunnel.

    config system interface
        edit "port2"
            set vdom "root"
            set ip 10.100.77.0 255.255.255.0
        next
    end
  4. Configure the import certificate and its CA certificate information.

    The certificate and its CA certificate must be imported on the remote peer FortiGate and on the primary FortiGate before configuring IPsec VPN tunnels. If the built-in Fortinet_Factory certificate and the Fortinet_CA CA certificate are used for authentication, you can skip this step.

    config vpn certificate local
        edit "test1"
            ...
            set range global
        next
    end
    config vpn certificate ca
        edit "CA_Cert_1"
            ...
            set range global
        next
    end
  5. Configure the peer user.

    The peer user is used in the IPsec VPN tunnel peer setting to authenticate the remote peer FortiGate.

    • If not using the built-in Fortinet_Factory certificate and Fortinet_CA CA certificate:

      config user peer
          edit "peer1"
              set ca "CA_Cert_1"
          next
      end
    • If the built-in Fortinet_Factory certificate and Fortinet_CA CA certificate are used for authentication, the peer user must be configured based on Fortinet_CA:

      config user peer
          edit "peer1"
              set ca "Fortinet_CA"
          next
      end
  6. Configure the IPsec phase1-interface.

    config vpn ipsec phase1-interface
        edit "HQ2B2"
            set interface "port1"
            set ike-version 2
            set authmethod signature
            set net-device enable
            set proposal aes128-sha256 aes256-sha256 aes128-sha1 aes256-sha1
            set remote-gw 10.100.68.5
            set certificate "test1"
            set peer "peer1"
        next
    end
  7. Configure the IPsec phase2-interface.

    config vpn ipsec phase2-interface
        edit "HQ2B2"
            set phase1name "HQ2B2 "
            set proposal aes128-sha1 aes256-sha1 aes128-sha256 aes256-sha256 aes128gcm aes256gcm chacha20poly1305
            set auto-negotiate enable
            set src-addr-type name
            set dst-addr-type name
            set src-name "10.100.77.0"
            set dst-name "10.2.0.0"
        next
    end
  8. Configure the static routes.

    Two static routes are added to reach the remote protected subnet. The blackhole route is important to ensure that IPsec traffic does not match the default route when the IPsec tunnel is down.

    config router static
        edit 2
            set dst 10.20.0.0 255.255.255.0
            set device "HQ2B2"
        next
        edit 3
            set dst 10.20.0.0 255.255.255.0
            set blackhole enable
            set distance 254
        next
    end
  9. Configure two firewall policies to allow bidirectional IPsec traffic flow over the IPsec VPN tunnel.

    config firewall policy
        edit 1
            set name "inbound"
            set srcintf "HQ2B2"
            set dstintf "port2"
            set srcaddr "10.2.0.0"
            set dstaddr "10.100.77.0"
            set action accept
            set schedule "always"
            set service "ALL"
        next
        edit 2
            set name "outbound"
            set srcintf "port2"
            set dstintf "HQ2B2"
            set srcaddr "10.100.77.0"
            set dstaddr "10.2.0.0"
            set action accept
            set schedule "always"
            set service "ALL"
        next
    end
To configure HQ2 for IPsec VPN authenticating a remote FortiGate peer with a digital certificate using the CLI:
  1. Configure the WAN interface and default route.

    config system interface 
        edit "port1"
            set vdom "root"
            set ip 10.100.68.5 255.255.255.0
        next
    end
    config router static
        edit 1
            set gateway 10.100.68.2
            set device "port1"
        next
    end
  2. Configure address objects for internal protected networks.

    config firewall address
        edit "10.2.0.0"
            set subnet 10.2.0.0 255.255.255.0
        next
    end
    config firewall address
        edit "10.100.77.0"
            set subnet 10.100.77.0 255.255.255.0
        next
    end
  3. Configure the internal (protected subnet) interface.

    config system interface
        edit "port3"
            set vdom "root"
            set ip 10.2.0.0 255.255.255.0
        next
    end
  4. Configure the import certificate and its CA certificate information.

    config vpn certificate local
        edit "test2"
            ...
            set range global
        next
    end
    config vpn certificate ca
        edit "CA_Cert_1"
            ...
            set range global
        next
    end
  5. Configure the peer user.

    • If not using the built-in Fortinet_Factory certificate and Fortinet_CA CA certificate:

      config user peer
          edit "peer2"
              set ca "CA_Cert_1"
          next
      end
    • If the built-in Fortinet_Factory certificate and Fortinet_CA CA certificate are used for authentication, the peer user must be configured based on Fortinet_CA:

      config user peer
          edit "peer2"
              set ca "Fortinet_CA"
          next
      end
  6. Configure the IPsec phase1-interface.

    config vpn ipsec phase1-interface
        edit "HQ2B2"
            set interface "port1"
            set ike-version 2
            set authmethod signature
            set net-device enable
            set proposal aes128-sha256 aes256-sha256 aes128-sha1 aes256-sha1
            set remote-gw 10.100.68.5
            set certificate "test1"
            set peer "peer1"
        next
    end
  7. Configure the IPsec phase2-interface.

    config vpn ipsec phase2-interface
        edit "B2toHQ"
            set phase1name "B2toHQ"
            set proposal aes128-sha1 aes256-sha1 aes128-sha256 aes256-sha256 aes128gcm aes256gcm chacha20poly1305
            set auto-negotiate enable
            set src-addr-type name
            set dst-addr-type name
            set src-name "10.2.0.0"
            set dst-name "10.100.77.0"
        next
    end
  8. Configure the static routes.

    config router static
        edit 2
            set dst 10.100.77.0 255.255.255.0
            set device "B2toHQ"
        next
        edit 3
            set dst 10.100.77.0 255.255.255.0
            set blackhole enable
            set distance 254
        next
    end
  9. Configure two firewall policies to allow bidirectional IPsec traffic flow over the IPsec VPN tunnel.

    config firewall policy
        edit 1
            set name "inbound"
            set srcintf "B2toHQ"
            set dstintf "port3"
            set srcaddr "10.100.77.0"
            set dstaddr "10.2.0.0"
            set action accept
            set schedule "always"
            set service "ALL"
        next
        edit 2
            set name "outbound"
            set srcintf "port3"
            set dstintf "B2toHQ"
            set srcaddr "10.2.0.0"
            set dstaddr "10.100.77.0"
            set action accept
            set schedule "always"
            set service "ALL"
        next
    end
To verify the tunnel status in the GUI:
  1. On FortiGate HQ1, go to Dashboard > Network and expand the IPsec widget.

  2. Find the new tunnel, HQ2B2 in this example, and check that both Phase 1 and Phase 2 Tunnel are up.

  3. Verify the tunnel status on HQ2 in the same way.

To verify the tunnel status in the CLI:
  1. On FortiGate HQ1, run the following command:

    # diagnose vpn ike gateway list name HQ2B2
    vd: root/0
    name: HQ2B2
    version: 2
    interface: port1 3
    addr: 10.100.64.101:500 -> 10.100.68.5:500
    tun_id: 10.100.68.5/::10.100.68.5
    remote_location: 0.0.0.0
    network-id: 0
    transport: UDP
    created: 852804s ago
    peer-id: 10.100.68.5
    peer-id-auth: no
    pending-queue: 0
    PPK: no
    IKE SA: created 1/11  established 1/11  time 0/820/9010 ms
    IPsec SA: created 1/21  established 1/21  time 0/433/9010 ms
    
    id/spi: 8895 45e69522bd784183/69be2940ae314677
    direction: responder
    status: established 77898-77898s ago = 0ms
    proposal: aes128-sha256
    child: yes
    SK_ei: 07446ef38bd406fa-18e45bec886a2bd3
    SK_er: b940f4338b27f369-7beaa308b7241a1b
    SK_ai: 61eeb720d062c70b-e606340beab6f9d5-3a4da2966373ab15-e5766540cf6c7dd1
    SK_ar: bbdd888b98dbda7b-669da7a726ce2148-3f08940f802f580c-52b6ef93f48672aa
    message-id sent/recv: 0/1783
    QKD: no
    lifetime/rekey: 86400/8231
    DPD sent/recv: 00000000/00000000
    peer-id: 10.100.68.5

    Note that HQ1 acted as the responder, and established the tunnel with remote peer 10.100.68.5 over UDP/500.

  2. On FortiGate HQ2, run the following command:

    # diagnose vpn ike gateway list name B2toHQ 
    vd: root/0
    name: B2toHQ
    version: 2
    interface: port1 3
    addr: 10.100.68.5:500 -> 10.100.64.101:500
    tun_id: 10.100.64.101/::10.100.64.101
    remote_location: 0.0.0.0
    network-id: 0
    transport: UDP
    created: 853181s ago
    peer-id: 10.100.64.101
    peer-id-auth: no
    pending-queue: 0
    PPK: no
    IKE SA: created 1/11  established 1/11  time 0/5/10 ms
    IPsec SA: created 1/21  established 1/21  time 0/0/10 ms
    
    id/spi: 5788 45e69522bd784183/69be2940ae314677
    direction: initiator
    status: established 78281-78281s ago = 10ms
    proposal: aes128-sha256
    child: yes
    SK_ei: 07446ef38bd406fa-18e45bec886a2bd3
    SK_er: b940f4338b27f369-7beaa308b7241a1b
    SK_ai: 61eeb720d062c70b-e606340beab6f9d5-3a4da2966373ab15-e5766540cf6c7dd1
    SK_ar: bbdd888b98dbda7b-669da7a726ce2148-3f08940f802f580c-52b6ef93f48672aa
    message-id sent/recv: 1792/0
    QKD: no
    lifetime/rekey: 86400/7818
    DPD sent/recv: 00001ed7/00001ed7
    peer-id: 10.100.64.101

    Note that HQ2 acted as the initiator, and established the tunnel with remote peer 10.100.64.101 over UDP/500.

To verify traffic through the IPsec tunnel:
  1. On a PC connected behind the port2 interface of HQ1, initiate ICMP traffic to the 10.2.0.0/24 network and verify that traffic goes through:

    root@dmz-public-server:~# ping 10.2.0.7
    PING 10.2.0.7 (10.2.0.7) 56(84) bytes of data.
    64 bytes from 10.2.0.7: icmp_seq=1 ttl=62 time=9.84 ms
    64 bytes from 10.2.0.7: icmp_seq=2 ttl=62 time=0.808 ms
    
  2. Verify the traffic on HQ1:

    # diagnose sniffer packet any 'host 10.2.0.7' 4 0 l
    Using Original Sniffing Mode
    interfaces=[any]
    filters=[host 10.2.0.7]
    2024-11-05 12:06:05.509027 port2 in 10.100.77.101 -> 10.2.0.7: icmp: echo request
    2024-11-05 12:06:05.509074 HQ2B2 out 10.100.77.101 -> 10.2.0.7: icmp: echo request
    2024-11-05 12:06:05.518607 HQ2B2 in 10.2.0.7 -> 10.100.77.101: icmp: echo reply
    2024-11-05 12:06:05.518632 port2 out 10.2.0.7 -> 10.100.77.101: icmp: echo reply
    

    The ICMP request packets are received on port2 and routed to the HQ2B2 tunnel. ICMP reply packets are received on the HQ2B2 tunnel and routed back out port2.

  3. Verify the traffic on HQ12:

    # diagnose sniffer packet any 'host 10.100.77.101' 4 0 l
    Using Original Sniffing Mode
    interfaces=[any]
    filters=[host 10.100.77.101]
    2024-11-05 12:06:05.509711 B2toHQ in 10.100.77.101 -> 10.2.0.7: icmp: echo request
    2024-11-05 12:06:05.509791 port3 out 10.100.77.101 -> 10.2.0.7: icmp: echo request
    2024-11-05 12:06:05.518809 port3 in 10.2.0.7 -> 10.100.77.101: icmp: echo reply
    2024-11-05 12:06:05.518899 B2toHQ out 10.2.0.7 -> 10.100.77.101: icmp: echo reply 
    

    The ICMP request is received on the B2toHQ tunnel and routed to port3. The ICMP reply is received on port3 and routed back out the B2toHQ.

  4. Optionally, run real time IKE debug using appropriate filters for troubleshooting if the IPsec tunnel does not come up:

    diagnose debug application ike -1

    If the remote FortiGate certificate cannot be validated, the following error is shown in the debug output:

    ike 0: to_HQ2:15314: certificate validation failed