This topic includes examples that incorporate several SNMP settings:

Example 1: SNMP traps for monitoring interface status using SNMP v3 user

This configuration enables the SNMP manager (172.16.200.55) to receive notifications when a FortiGate port either goes down or is brought up. The SNMP manager can also query the current status of the FortiGate port.

To configure SNMP for monitoring interface status in the GUI:
  1. Configure interface access:

    1. Go to Network > Interfaces and edit port1.

    2. In the Administrative Access options, enable SNMP.

    3. Click OK.

  2. Configure the SNMP agent:

    1. Go to System > SNMP.

    2. Enable SNMP Agent and enter the following:

      Description

      Branch

      Location

      Burnaby

      Contact Info

      Jane Doe

    3. Click Apply.

  3. Configure an SNMP v3 user:

    1. Go to System > SNMP.

    2. In the SNMP v3 table, click Create New.

    3. Configure the following:

      User Name

      Interface_Status

      Security Level

      Authentication

      Authentication Algorithm

      SHA1

      Password

      *******

      Hosts IP Address

      172.16.200.55

    4. Click OK.

To configure SNMP for monitoring interface status in the CLI:
  1. Configure interface access:

    config system interface
        edit port1
            append allowaccess snmp
        next
    end
    
  2. Configure the SNMP agent:

    config system snmp sysinfo
        set status enable
        set description Branch
        set contact-info Jane Doe
        set location Burnaby
    end
  3. Configure an SNMP v3 user:

    config system snmp user
        edit "Interface_Status"
            set notify-hosts 172.16.200.55
            set security-level auth-no-priv
            set auth-proto sha
            set auth-pwd ********************
        next
    end
Verification
  1. Start the packet capture on interface port1 with the filter set to port 162. See Using the packet capture tool for more information.

  2. Turn off one of the FortiGate interface statuses to down, in this case, port2.

  3. Save the packet capture.

    The SNMP v3 trap is transmitted from port1 to the SNMP manager. Note that msgAuthenticationParameters is configured, indicating that authentication is active. The absence of msgPrivacyParameters suggests that encryption is not configured. This is further confirmed by plaintext in msgData.

  4. Verify that the SNMP manager has received the trap. See Important SNMP traps for an example of a trap.

  5. Verify that the SNMP manager can successfully query and receive receive a response on the current status of the FortiGate ports:

    # snmpwalk -v3 -u Interface_Status  -l authNoPriv -a SHA -A xxxxxxxx 172.16.200.1 1.3.6.1.2.1.2.2.1.8
    iso.3.6.1.2.1.2.2.1.8.1 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.2 = INTEGER: 2
    iso.3.6.1.2.1.2.2.1.8.3 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.4 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.5 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.6 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.7 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.8 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.9 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.10 = INTEGER: 1

Example 2: SNMP traps and query for monitoring DHCP pool using SNMP v3 user

This configuration enables the SNMP manager (172.16.200.55) to receive DHCP-related notifications from FortiGate.

The SNMP DHCP event contains three traps and one query.

Traps are sent when:

  • DHCP server IP pool usage reaches 90%

  • DHCP server detect an IP address that is already in use

  • DHCP client receives DHCP NAK

SNMP queries are accepted for DHCP lease usage information (OID = 1.3.6.1.4.1.12356.101.23). The query result is based on the leased out percentage.

To configure SNMP for monitoring DHCP pool in the GUI:
  1. Configure interface access:

    1. Go to Network > Interfaces and edit port1.

    2. In the Administrative Access options, enable SNMP.

    3. Click OK.

  2. Configure the SNMP agent:

    1. Go to System > SNMP.

    2. Enable SNMP Agent and enter the following:

      Description

      Branch

      Location

      Burnaby

      Contact Info

      Jane Doe

    3. Click Apply.

  3. Configure an SNMP v3 user:

    1. Go to System > SNMP.

    2. In the SNMP v3 table, click Create New.

    3. Configure the following:

      User Name

      DHCP_Status

      Security Level

      Authentication

      Authentication Algorithm

      SHA384

      Password

      *******

      Private

      Enabled

      Encryption Algorithm

      AES256

      Password

      *******

      Hosts IP Address

      172.16.200.55

    4. Click OK.

To configure SNMP for monitoring the DHCP pool in the CLI:
  1. Configure interface access:

    config system interface
        edit port1
            append allowaccess snmp
        next
    end
    
  2. Configure the SNMP agent:

    config system snmp sysinfo
        set status enable
        set description Branch
        set contact-info Jane Doe
        set location Burnaby
    end
  3. Configure an SNMP v3 user:

    config system snmp user
        edit "DHCP_Status"
            set notify-hosts 172.16.200.55
            set security-level auth-priv
            set auth-proto sha384
            set auth-pwd ********************
            set priv-proto aes256
            set priv-pwd *********************
        next
    end
Verification
  1. Start the packet capture on interface port1 with the filter set to port 162. See Using the packet capture tool for more information.

  2. Overload the DHCP server IP pool.

  3. Save the packet capture.

    The SNMP v3 trap is transmitted from port1 to the SNMP manager. Note that both msgAuthenticationParameters and msgPrivacyParameters are set up, indicating that authentication and encryption are active. This is further confirmed by encryptedPDU in msgData.

  4. Verify that the SNMP manager has received the trap. See Important SNMP traps for an example of a trap.

  5. Verify that the SNMP manager can successfully query and receive DHCP lease usage information for FortiGate:

    # snmpwalk -v3 -u DHCP_Status  -l authPriv -a SHA384 -A xxxxxxxx -x AES256 -X xxxxxxxx 172.16.200.1 1.3.6.1.4.1.12356.101.23
    iso.3.6.1.4.1.12356.101.23.1.1.0 = INTEGER: 6
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.1 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.2 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.3 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.4 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.5 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.6 = INTEGER: 100

Example 3: Enabling the INDEX extension

In the following example, the same IP address will be set on different ports in two VDOMs. The ipAddrTable SNMP Tree output will then be reviewed before and after enabling the append-index command.

Note

When the append-index command is enabled:

  • VDOM and interface indexes are appended as the INDEX extension in RFC tables.

  • In multi-VDOM mode, duplicated IP addresses in different VDOMs will result in multiple entries in the RFC table.

When the append-index command is disabled:

  • VDOM and interface indexes are not appended in RFC tables.

  • In multi-VDOM mode, duplicated IP addresses in different VDOMs will only be presented once in the RFC table.

To enable the INDEX extension:
  1. In two different VDOMs, set the same address on two different ports.

    config system interface
        edit "port3"
            set vdom "vdom1"
            set ip 10.1.1.1 255.255.255.0
            set type physical
            set snmp-index 5
        next
    end
    config system interface
        edit "port4"
            set vdom "root"
            set ip 10.1.1.1 255.255.255.0
            set type physical
            set snmp-index 6
        next
    end
  2. Configure the SNMP information but do not enable the INDEX extension.

    config system snmp sysinfo
        set status enable
        set description "REGR-SYS"
    end
  3. On your PC, review the ipAddrTable SNMP Tree (OID 1.3.6.1.2.1.4.20). The IP address 10.1.1.1 is only displayed once.

    snmpwalk -v2c -c REGR-SYS 172.16.200.1 1.3.6.1.2.1.4.20
    
    IP-MIB::ipAdEntAddr.10.1.1.1 = IpAddress: 10.1.1.1
    IP-MIB::ipAdEntAddr.10.255.1.1 = IpAddress: 10.255.1.1
    IP-MIB::ipAdEntAddr.172.16.200.1 = IpAddress: 172.16.200.1
    IP-MIB::ipAdEntAddr.192.168.1.99 = IpAddress: 192.168.1.99
    IP-MIB::ipAdEntIfIndex.10.1.1.1 = INTEGER: 5
    IP-MIB::ipAdEntIfIndex.10.255.1.1 = INTEGER: 39
    IP-MIB::ipAdEntIfIndex.172.16.200.1 = INTEGER: 3
    IP-MIB::ipAdEntIfIndex.192.168.1.99 = INTEGER: 2
    IP-MIB::ipAdEntNetMask.10.1.1.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.10.255.1.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.172.16.200.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.192.168.1.99 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntBcastAddr.10.1.1.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.10.255.1.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.172.16.200.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.192.168.1.99 = INTEGER: 1
    IP-MIB::ipAdEntReasmMaxSize.10.1.1.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.10.255.1.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.172.16.200.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.192.168.1.99 = INTEGER: 65535
  4. Enable the INDEX extension.

    config system snmp sysinfo
        set status enable
        set description "REGR-SYS"
        set append-index enable
    end
  5. Review the ipAddrTable SNMP Tree (OID 1.3.6.1.2.1.4.20) again. The IP address 10.1.1.1 is now displayed twice.

    snmpwalk -v2c -c REGR-SYS 172.16.200.1 1.3.6.1.2.1.4.20
    
    IP-MIB::ipAdEntAddr.10.1.1.1.1 = IpAddress: 10.1.1.1
    IP-MIB::ipAdEntAddr.10.1.1.1.2 = IpAddress: 10.1.1.1
    IP-MIB::ipAdEntAddr.10.255.1.1.1 = IpAddress: 10.255.1.1
    IP-MIB::ipAdEntAddr.172.16.200.1.2 = IpAddress: 172.16.200.1
    IP-MIB::ipAdEntAddr.192.168.1.99.1 = IpAddress: 192.168.1.99
    IP-MIB::ipAdEntIfIndex.10.1.1.1.1 = INTEGER: 6
    IP-MIB::ipAdEntIfIndex.10.1.1.1.2 = INTEGER: 5
    IP-MIB::ipAdEntIfIndex.10.255.1.1.1 = INTEGER: 39
    IP-MIB::ipAdEntIfIndex.172.16.200.1.2 = INTEGER: 3
    IP-MIB::ipAdEntIfIndex.192.168.1.99.1 = INTEGER: 2
    IP-MIB::ipAdEntNetMask.10.1.1.1.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.10.1.1.1.2 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.10.255.1.1.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.172.16.200.1.2 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.192.168.1.99.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntBcastAddr.10.1.1.1.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.10.1.1.1.2 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.10.255.1.1.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.172.16.200.1.2 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.192.168.1.99.1 = INTEGER: 1
    IP-MIB::ipAdEntReasmMaxSize.10.1.1.1.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.10.1.1.1.2 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.10.255.1.1.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.172.16.200.1.2 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.192.168.1.99.1 = INTEGER: 65535

SNMP examples

SNMP examples

This topic includes examples that incorporate several SNMP settings:

Example 1: SNMP traps for monitoring interface status using SNMP v3 user

This configuration enables the SNMP manager (172.16.200.55) to receive notifications when a FortiGate port either goes down or is brought up. The SNMP manager can also query the current status of the FortiGate port.

To configure SNMP for monitoring interface status in the GUI:
  1. Configure interface access:

    1. Go to Network > Interfaces and edit port1.

    2. In the Administrative Access options, enable SNMP.

    3. Click OK.

  2. Configure the SNMP agent:

    1. Go to System > SNMP.

    2. Enable SNMP Agent and enter the following:

      Description

      Branch

      Location

      Burnaby

      Contact Info

      Jane Doe

    3. Click Apply.

  3. Configure an SNMP v3 user:

    1. Go to System > SNMP.

    2. In the SNMP v3 table, click Create New.

    3. Configure the following:

      User Name

      Interface_Status

      Security Level

      Authentication

      Authentication Algorithm

      SHA1

      Password

      *******

      Hosts IP Address

      172.16.200.55

    4. Click OK.

To configure SNMP for monitoring interface status in the CLI:
  1. Configure interface access:

    config system interface
        edit port1
            append allowaccess snmp
        next
    end
    
  2. Configure the SNMP agent:

    config system snmp sysinfo
        set status enable
        set description Branch
        set contact-info Jane Doe
        set location Burnaby
    end
  3. Configure an SNMP v3 user:

    config system snmp user
        edit "Interface_Status"
            set notify-hosts 172.16.200.55
            set security-level auth-no-priv
            set auth-proto sha
            set auth-pwd ********************
        next
    end
Verification
  1. Start the packet capture on interface port1 with the filter set to port 162. See Using the packet capture tool for more information.

  2. Turn off one of the FortiGate interface statuses to down, in this case, port2.

  3. Save the packet capture.

    The SNMP v3 trap is transmitted from port1 to the SNMP manager. Note that msgAuthenticationParameters is configured, indicating that authentication is active. The absence of msgPrivacyParameters suggests that encryption is not configured. This is further confirmed by plaintext in msgData.

  4. Verify that the SNMP manager has received the trap. See Important SNMP traps for an example of a trap.

  5. Verify that the SNMP manager can successfully query and receive receive a response on the current status of the FortiGate ports:

    # snmpwalk -v3 -u Interface_Status  -l authNoPriv -a SHA -A xxxxxxxx 172.16.200.1 1.3.6.1.2.1.2.2.1.8
    iso.3.6.1.2.1.2.2.1.8.1 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.2 = INTEGER: 2
    iso.3.6.1.2.1.2.2.1.8.3 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.4 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.5 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.6 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.7 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.8 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.9 = INTEGER: 1
    iso.3.6.1.2.1.2.2.1.8.10 = INTEGER: 1

Example 2: SNMP traps and query for monitoring DHCP pool using SNMP v3 user

This configuration enables the SNMP manager (172.16.200.55) to receive DHCP-related notifications from FortiGate.

The SNMP DHCP event contains three traps and one query.

Traps are sent when:

  • DHCP server IP pool usage reaches 90%

  • DHCP server detect an IP address that is already in use

  • DHCP client receives DHCP NAK

SNMP queries are accepted for DHCP lease usage information (OID = 1.3.6.1.4.1.12356.101.23). The query result is based on the leased out percentage.

To configure SNMP for monitoring DHCP pool in the GUI:
  1. Configure interface access:

    1. Go to Network > Interfaces and edit port1.

    2. In the Administrative Access options, enable SNMP.

    3. Click OK.

  2. Configure the SNMP agent:

    1. Go to System > SNMP.

    2. Enable SNMP Agent and enter the following:

      Description

      Branch

      Location

      Burnaby

      Contact Info

      Jane Doe

    3. Click Apply.

  3. Configure an SNMP v3 user:

    1. Go to System > SNMP.

    2. In the SNMP v3 table, click Create New.

    3. Configure the following:

      User Name

      DHCP_Status

      Security Level

      Authentication

      Authentication Algorithm

      SHA384

      Password

      *******

      Private

      Enabled

      Encryption Algorithm

      AES256

      Password

      *******

      Hosts IP Address

      172.16.200.55

    4. Click OK.

To configure SNMP for monitoring the DHCP pool in the CLI:
  1. Configure interface access:

    config system interface
        edit port1
            append allowaccess snmp
        next
    end
    
  2. Configure the SNMP agent:

    config system snmp sysinfo
        set status enable
        set description Branch
        set contact-info Jane Doe
        set location Burnaby
    end
  3. Configure an SNMP v3 user:

    config system snmp user
        edit "DHCP_Status"
            set notify-hosts 172.16.200.55
            set security-level auth-priv
            set auth-proto sha384
            set auth-pwd ********************
            set priv-proto aes256
            set priv-pwd *********************
        next
    end
Verification
  1. Start the packet capture on interface port1 with the filter set to port 162. See Using the packet capture tool for more information.

  2. Overload the DHCP server IP pool.

  3. Save the packet capture.

    The SNMP v3 trap is transmitted from port1 to the SNMP manager. Note that both msgAuthenticationParameters and msgPrivacyParameters are set up, indicating that authentication and encryption are active. This is further confirmed by encryptedPDU in msgData.

  4. Verify that the SNMP manager has received the trap. See Important SNMP traps for an example of a trap.

  5. Verify that the SNMP manager can successfully query and receive DHCP lease usage information for FortiGate:

    # snmpwalk -v3 -u DHCP_Status  -l authPriv -a SHA384 -A xxxxxxxx -x AES256 -X xxxxxxxx 172.16.200.1 1.3.6.1.4.1.12356.101.23
    iso.3.6.1.4.1.12356.101.23.1.1.0 = INTEGER: 6
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.1 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.2 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.3 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.4 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.5 = INTEGER: 0
    iso.3.6.1.4.1.12356.101.23.2.1.1.2.1.6 = INTEGER: 100

Example 3: Enabling the INDEX extension

In the following example, the same IP address will be set on different ports in two VDOMs. The ipAddrTable SNMP Tree output will then be reviewed before and after enabling the append-index command.

Note

When the append-index command is enabled:

  • VDOM and interface indexes are appended as the INDEX extension in RFC tables.

  • In multi-VDOM mode, duplicated IP addresses in different VDOMs will result in multiple entries in the RFC table.

When the append-index command is disabled:

  • VDOM and interface indexes are not appended in RFC tables.

  • In multi-VDOM mode, duplicated IP addresses in different VDOMs will only be presented once in the RFC table.

To enable the INDEX extension:
  1. In two different VDOMs, set the same address on two different ports.

    config system interface
        edit "port3"
            set vdom "vdom1"
            set ip 10.1.1.1 255.255.255.0
            set type physical
            set snmp-index 5
        next
    end
    config system interface
        edit "port4"
            set vdom "root"
            set ip 10.1.1.1 255.255.255.0
            set type physical
            set snmp-index 6
        next
    end
  2. Configure the SNMP information but do not enable the INDEX extension.

    config system snmp sysinfo
        set status enable
        set description "REGR-SYS"
    end
  3. On your PC, review the ipAddrTable SNMP Tree (OID 1.3.6.1.2.1.4.20). The IP address 10.1.1.1 is only displayed once.

    snmpwalk -v2c -c REGR-SYS 172.16.200.1 1.3.6.1.2.1.4.20
    
    IP-MIB::ipAdEntAddr.10.1.1.1 = IpAddress: 10.1.1.1
    IP-MIB::ipAdEntAddr.10.255.1.1 = IpAddress: 10.255.1.1
    IP-MIB::ipAdEntAddr.172.16.200.1 = IpAddress: 172.16.200.1
    IP-MIB::ipAdEntAddr.192.168.1.99 = IpAddress: 192.168.1.99
    IP-MIB::ipAdEntIfIndex.10.1.1.1 = INTEGER: 5
    IP-MIB::ipAdEntIfIndex.10.255.1.1 = INTEGER: 39
    IP-MIB::ipAdEntIfIndex.172.16.200.1 = INTEGER: 3
    IP-MIB::ipAdEntIfIndex.192.168.1.99 = INTEGER: 2
    IP-MIB::ipAdEntNetMask.10.1.1.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.10.255.1.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.172.16.200.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.192.168.1.99 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntBcastAddr.10.1.1.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.10.255.1.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.172.16.200.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.192.168.1.99 = INTEGER: 1
    IP-MIB::ipAdEntReasmMaxSize.10.1.1.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.10.255.1.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.172.16.200.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.192.168.1.99 = INTEGER: 65535
  4. Enable the INDEX extension.

    config system snmp sysinfo
        set status enable
        set description "REGR-SYS"
        set append-index enable
    end
  5. Review the ipAddrTable SNMP Tree (OID 1.3.6.1.2.1.4.20) again. The IP address 10.1.1.1 is now displayed twice.

    snmpwalk -v2c -c REGR-SYS 172.16.200.1 1.3.6.1.2.1.4.20
    
    IP-MIB::ipAdEntAddr.10.1.1.1.1 = IpAddress: 10.1.1.1
    IP-MIB::ipAdEntAddr.10.1.1.1.2 = IpAddress: 10.1.1.1
    IP-MIB::ipAdEntAddr.10.255.1.1.1 = IpAddress: 10.255.1.1
    IP-MIB::ipAdEntAddr.172.16.200.1.2 = IpAddress: 172.16.200.1
    IP-MIB::ipAdEntAddr.192.168.1.99.1 = IpAddress: 192.168.1.99
    IP-MIB::ipAdEntIfIndex.10.1.1.1.1 = INTEGER: 6
    IP-MIB::ipAdEntIfIndex.10.1.1.1.2 = INTEGER: 5
    IP-MIB::ipAdEntIfIndex.10.255.1.1.1 = INTEGER: 39
    IP-MIB::ipAdEntIfIndex.172.16.200.1.2 = INTEGER: 3
    IP-MIB::ipAdEntIfIndex.192.168.1.99.1 = INTEGER: 2
    IP-MIB::ipAdEntNetMask.10.1.1.1.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.10.1.1.1.2 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.10.255.1.1.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.172.16.200.1.2 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntNetMask.192.168.1.99.1 = IpAddress: 255.255.255.0
    IP-MIB::ipAdEntBcastAddr.10.1.1.1.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.10.1.1.1.2 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.10.255.1.1.1 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.172.16.200.1.2 = INTEGER: 1
    IP-MIB::ipAdEntBcastAddr.192.168.1.99.1 = INTEGER: 1
    IP-MIB::ipAdEntReasmMaxSize.10.1.1.1.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.10.1.1.1.2 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.10.255.1.1.1 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.172.16.200.1.2 = INTEGER: 65535
    IP-MIB::ipAdEntReasmMaxSize.192.168.1.99.1 = INTEGER: 65535