Fortinet white logo
Fortinet white logo

Administration Guide

Using FortiManager as a local FortiGuard server

Using FortiManager as a local FortiGuard server

FortiManager can provide a local FortiGuard server with port 443 access.

Anycast FortiGuard settings force the rating process to use port 443, even with an override server. Using a unique address in the same subnet as the FortiManager access IP address, the FortiManager can provide local FortiGuard updates and rating access with a dedicated IP address and port 443.

Caution

On FortiManager, use the Bind to IP addresses for the update and rating services over TCP/443.

The Bind to IP address does not need to be configured for update services if the default port was not changed to TCP/443. See Configuring network interfaces in the FortiManager Administration Guide for more information.

To use a FortiManager as a local FortiGuard server in the GUI:
  1. Go to System > FortiGuard

  2. In the Override FortiGuard Servers table, click Create New. The Create New Override FortiGuard Server pane opens.

  3. Select the server address type: IPv4, IPv6, or FQDN.

  4. Enter the FortiManager address in the Address field.

  5. Select the type of server: AntiVirus & IPS Updates, Filtering, or Both.

  6. Click OK.

  7. Click Create New again to add a second override FortiManager for filtering.

  8. Click OK, then click Apply.

To use a FortiManager as a local FortiGuard server in the CLI:
config system central-management
    set type fortimanager
    set fmg "172.18.37.148"
    config server-list
        edit 1
            set server-type update
            set server-address 172.18.37.150
        next
        edit 2
            set server-type rating
            set server-address 172.18.37.149
        next
    end
    set fmg-update-port 443
    set include-default-servers enable
end

When fmg-update-port is set to 443, the update process will use port 443 to connect to the override update server, which is the local FortiGuard server in the FortiManager. If this is not set, the update process will use port 8890, and the server address setting must be the FortiManager access IP address. Override FortiGuard services come from the server list that is the local FortiGuard server in the FortiManager, and use the traditional, non-OCSP TLS handshake. If override servers in the FortiManager are not available, the default FortiGuard servers are connected, and the anycast OCSP TLS handshake is used.

The FortiManager IP address used in set server-address (for example, set server-address 172.18.37.149) corresponds to the Bind to IP setting configured on the FortiManager interface.

HA considerations

When FortiGate and FortiManager units are both in high availability (HA) clusters, and FortiGate is using FortiManager as an update server, you must configure the following secondary IP addresses:

  • Configure secondary IP addresses for the service on both FortiManager units in the HA cluster

  • Configure FortiGate to use the secondary FortiManager IP addresses.

In this example, the primary FortiManager unit is configured to use the secondary IP address of 10.4.1.204 for the rating service, and the secondary FortiManager unit is configured to use the secondary IP address of 10.4.1.205 for the rating service. FortiGate is configured to use the secondary IP addresses on FortiManager.

To configure FortiManager units in an HA cluster as web filter rating servers:
  1. On the primary FortiManager in the HA cluster, configure a secondary IP address for the rating service:

    The set rating-service-ip is set to the secondary IP address for the rating query.

    config system interface
        edit "port1"
            set ip 10.4.1.104 255.255.0.0
            set allowaccess ping https ssh snmp http webservice
            set serviceaccess fgtupdates fclupdates webfilter-antispam
            set rating-service-ip 10.4.1.204 255.255.0.0 
            set type physical
        next
    end
  2. On the secondary FortiManager in the HA cluster, configure a secondary IP address for the rating service:

    The set rating-service-ip is set to the secondary IP address for the rating query.

    config system interface
        edit "port1"
            set ip 10.4.1.105 255.255.0.0
            set allowaccess ping https ssh snmp http webservice
            set serviceaccess fgtupdates fclupdates webfilter-antispam
            set rating-service-ip 10.4.1.205 255.255.0.0
            set type physical
        next
    end
  3. On both the primary and secondary FortiManager units in the HA cluster, enable web filter query:

    config fmupdate service
        set query-webfilter enable
    end
  4. On both the primary and secondary FortiManager units in the HA cluster, enable all web filter logs:

    config fmupdate web-spam fgd-setting
        set wf-log all
    end
  5. As needed, run the diagnose debug application fgdsvr 255 command.

    For additional details, use shell and run bash$ tail -f /var/log/fgdsvr.log to display the incoming URL queries.

To configure FortiGate:
  1. On FortiGate, configure central management to use the secondary FortiManager IP addresses for the rating service:

    The set rating-service-ip is set to the secondary IP address on the primary and secondary FortiManager units in the HA cluster.

    config system central-management
        set type fortimanager
        config server-list
            edit 1
                set server-type update
                set server-address 10.4.1.104              
            next
            edit 3
                set server-type update
                set server-address 10.4.1.105
            next
            edit 2
                set server-type rating
                set server-address 10.4.1.204
            next
            edit 4
                set server-type rating
                set server-address 10.4.1.205
            next
        end
        set include-default-servers disable
    end
  2. Disable Anycast:

    config system fortiguard
        set fortiguard-anycast disable 
    end
    
  3. As needed, run the following diagnose commands:

    • Run diagnose debug app urlfilter -1 to show the rating query response.

    • Run diagnose debug rating to show the rating service information.

Using FortiManager as a local FortiGuard server

Using FortiManager as a local FortiGuard server

FortiManager can provide a local FortiGuard server with port 443 access.

Anycast FortiGuard settings force the rating process to use port 443, even with an override server. Using a unique address in the same subnet as the FortiManager access IP address, the FortiManager can provide local FortiGuard updates and rating access with a dedicated IP address and port 443.

Caution

On FortiManager, use the Bind to IP addresses for the update and rating services over TCP/443.

The Bind to IP address does not need to be configured for update services if the default port was not changed to TCP/443. See Configuring network interfaces in the FortiManager Administration Guide for more information.

To use a FortiManager as a local FortiGuard server in the GUI:
  1. Go to System > FortiGuard

  2. In the Override FortiGuard Servers table, click Create New. The Create New Override FortiGuard Server pane opens.

  3. Select the server address type: IPv4, IPv6, or FQDN.

  4. Enter the FortiManager address in the Address field.

  5. Select the type of server: AntiVirus & IPS Updates, Filtering, or Both.

  6. Click OK.

  7. Click Create New again to add a second override FortiManager for filtering.

  8. Click OK, then click Apply.

To use a FortiManager as a local FortiGuard server in the CLI:
config system central-management
    set type fortimanager
    set fmg "172.18.37.148"
    config server-list
        edit 1
            set server-type update
            set server-address 172.18.37.150
        next
        edit 2
            set server-type rating
            set server-address 172.18.37.149
        next
    end
    set fmg-update-port 443
    set include-default-servers enable
end

When fmg-update-port is set to 443, the update process will use port 443 to connect to the override update server, which is the local FortiGuard server in the FortiManager. If this is not set, the update process will use port 8890, and the server address setting must be the FortiManager access IP address. Override FortiGuard services come from the server list that is the local FortiGuard server in the FortiManager, and use the traditional, non-OCSP TLS handshake. If override servers in the FortiManager are not available, the default FortiGuard servers are connected, and the anycast OCSP TLS handshake is used.

The FortiManager IP address used in set server-address (for example, set server-address 172.18.37.149) corresponds to the Bind to IP setting configured on the FortiManager interface.

HA considerations

When FortiGate and FortiManager units are both in high availability (HA) clusters, and FortiGate is using FortiManager as an update server, you must configure the following secondary IP addresses:

  • Configure secondary IP addresses for the service on both FortiManager units in the HA cluster

  • Configure FortiGate to use the secondary FortiManager IP addresses.

In this example, the primary FortiManager unit is configured to use the secondary IP address of 10.4.1.204 for the rating service, and the secondary FortiManager unit is configured to use the secondary IP address of 10.4.1.205 for the rating service. FortiGate is configured to use the secondary IP addresses on FortiManager.

To configure FortiManager units in an HA cluster as web filter rating servers:
  1. On the primary FortiManager in the HA cluster, configure a secondary IP address for the rating service:

    The set rating-service-ip is set to the secondary IP address for the rating query.

    config system interface
        edit "port1"
            set ip 10.4.1.104 255.255.0.0
            set allowaccess ping https ssh snmp http webservice
            set serviceaccess fgtupdates fclupdates webfilter-antispam
            set rating-service-ip 10.4.1.204 255.255.0.0 
            set type physical
        next
    end
  2. On the secondary FortiManager in the HA cluster, configure a secondary IP address for the rating service:

    The set rating-service-ip is set to the secondary IP address for the rating query.

    config system interface
        edit "port1"
            set ip 10.4.1.105 255.255.0.0
            set allowaccess ping https ssh snmp http webservice
            set serviceaccess fgtupdates fclupdates webfilter-antispam
            set rating-service-ip 10.4.1.205 255.255.0.0
            set type physical
        next
    end
  3. On both the primary and secondary FortiManager units in the HA cluster, enable web filter query:

    config fmupdate service
        set query-webfilter enable
    end
  4. On both the primary and secondary FortiManager units in the HA cluster, enable all web filter logs:

    config fmupdate web-spam fgd-setting
        set wf-log all
    end
  5. As needed, run the diagnose debug application fgdsvr 255 command.

    For additional details, use shell and run bash$ tail -f /var/log/fgdsvr.log to display the incoming URL queries.

To configure FortiGate:
  1. On FortiGate, configure central management to use the secondary FortiManager IP addresses for the rating service:

    The set rating-service-ip is set to the secondary IP address on the primary and secondary FortiManager units in the HA cluster.

    config system central-management
        set type fortimanager
        config server-list
            edit 1
                set server-type update
                set server-address 10.4.1.104              
            next
            edit 3
                set server-type update
                set server-address 10.4.1.105
            next
            edit 2
                set server-type rating
                set server-address 10.4.1.204
            next
            edit 4
                set server-type rating
                set server-address 10.4.1.205
            next
        end
        set include-default-servers disable
    end
  2. Disable Anycast:

    config system fortiguard
        set fortiguard-anycast disable 
    end
    
  3. As needed, run the following diagnose commands:

    • Run diagnose debug app urlfilter -1 to show the rating query response.