Fortinet white logo
Fortinet white logo

Administration Guide

Interface-based traffic shaping profile

Interface-based traffic shaping profile

A traffic shaping policy can be used for interface-based traffic shaping by organizing traffic into 30 class IDs. The shaping profile defines the percentage of the interface bandwidth that is allocated to each class. Each traffic class ID is shaped to the assigned speed according to the outgoing bandwidth limit configured to the interface.

Traffic classification

A shaping policy classifies traffic and organizes it into different class IDs, based on matching criteria. For traffic matching a criteria, you can choose to put it into 30 different shaping classes, identified by class ID 2 to 31.

You must select an outgoing interface for the traffic. The shaping policy is only applied when the traffic goes to one of the selected outgoing interfaces.

Criterion

Description

Source

  • Address: match the source address of the traffic to the selected address or address group.
  • User: use the user credentials of the traffic to match the selected user or user group. At least one address, address group, or internet service must also be selected.
  • Internet service: match the traffic to the selected internet service. Internet services cannot be used if addresses or address or groups are used.

Destination

  • Address: match the destination address of the traffic to the selected address or address group.
  • Internet service: match the traffic to the selected internet service. Internet services cannot be used if addresses or address or groups are used.

Schedule

Match the current date and time to the selected schedule. You can select a one-time schedule, recurring schedule, or schedule group. This setting is optional.

Service

Match the service of the traffic to the selected service or service group.

Application

Match the application of the traffic to the selected application, application category, or application group.

Application control must be enabled in the related firewall policy to know the application of the traffic. See Application control for more information.

URL category

Match the URL of the traffic to the selected URL category.

Web filter must be enabled in the related firewall policy to know the URL of the traffic. See Web filter for more information.

Note

When multiple items are selected in one criterion, it is considered a match when traffic matches any one of them.

Traffic prioritization

Shaping profiles define how different shaping classes of traffic are prioritized. For each class, you can define three prioritization strategies: guaranteed bandwidth, maximum bandwidth, and priority.

For each shaping profile, a default shaping class must be defined. Traffic is prioritized based on the default shaping group in the following two circumstances:

  • All traffic to the outgoing interface that does not match to any shaping policy
  • Traffic with a shaping group that is not defined in a shaping profile

Prioritization strategy

Description

Guaranteed bandwidth

The percentage of the link speed that is reserved for the shaping group.

The total guaranteed bandwidth for all shaping groups cannot exceed 100%.

Maximum bandwidth

The maximum percentage of the link speed that the shaping group can use.

Priority

The shaping class priority: top, critical, high, medium, or low. When groups are competing for bandwidth on the interface, the group with the higher priority wins.

Applying a shaping profile to an interface

Traffic shaping is accomplished by configuring the outgoing bandwidth and outgoing shaping profile on an interface. The shaping profile uses the outgoing bandwidth of the interface as the maximum link speed, and it only works when the outgoing bandwidth is configured.

This example shows how to apply interface-based traffic shaping to web and file accessing traffic according to a schedule:

  • The link speed of the wan1 interface is 10 Mb/s.
  • File access can use up to 2 Mb/s from 8:00 AM to 6:00 PM.
  • Web access can use 8 Mb/s from 8:00 AM to 6:00 PM.

Putting the traffic into shaping classes

To create a recurring schedule in the GUI:
  1. Go to Policy & Objects > Schedules.
  2. Click Create New > Schedule.
  3. Configure a recurring schedule called Day_Hours for everyday from 8:00 AM to 6:00 PM.
  4. Click OK.
To create a traffic shaping policy and class ID for the web accessing traffic in the GUI:
  1. Go to Policy & Objects > Traffic Shaping, select the Traffic Shaping Policies tab, and click Create New.
  2. Enter a name for the policy, such as web_access_day_hours.
  3. Enable Schedule and select the schedule you just created.
  4. Set Service to web accessing services, such as HTTP and HTTPS.
  5. Set Action to Assign Shaping Class ID, and Outgoing interface to wan1.
  6. Click the Traffic shaping class ID drop down then click Create.
  7. Enter an integer value for the ID (3) and a description for the Name, such as Web Access.
  8. Click OK.
  9. Select the class ID you just created for Traffic shaping class ID.

  10. Configure the remaining settings as required.
  11. Click OK.
To create a traffic shaping policy and class ID for the file accessing traffic in the GUI:
  1. Go to Policy & Objects > Traffic Shaping, select the Traffic Shaping Policies tab, and click Create New.
  2. Enter a name for the policy, such as file_access_day_hours.
  3. Enable Schedule and select the schedule you just created.
  4. Set Service to file accessing services, such as ASF3, FTP and SMB.
  5. Set Action to Assign Shaping Class ID, and Outgoing interface to wan1.
  6. Click the Traffic shaping class ID drop down then click Create.
  7. Enter an integer value for the ID (4) and a description for the Name, such as File Access.
  8. Click OK.
  9. Select the class ID you just created for Traffic shaping class ID.

  10. Configure the remaining settings as required.
  11. Click OK.
To put the traffic into shaping classes in the CLI:
  1. Create a recurring schedule:
    config firewall schedule recurring
        edit "Day_Hours"
            set start 08:00
            set end 18:00
            set day sunday monday tuesday wednesday thursday friday saturday
        next
    end
  2. Create the traffic class IDs:

    config firewall traffic-class
        edit 3
            set class-name "Web Access"
        next
        edit 4
            set class-name "File Access"
        next
    end
  3. Create the web and file accessing traffic shaping policies:
    config firewall shaping-policy
        edit 2
            set name "web_access_day_hours"
            set comment "Limit web accessing traffic to 8Mb/s in day time"
            set service "HTTP" "HTTPS"
            set schedule "Day_Hours"
            set dstintf "wan1"
            set class-id 3
            set srcaddr "all"
            set dstaddr "all"
        next
        edit 3
            set name "file_access_day_hours"
            set comment "Limit file accessing traffic to 2Mb/s during the day"
            set service "AFS3" "FTP" "FTP_GET" "FTP_PUT" "NFS" "SAMBA" "SMB" "TFTP"
            set schedule "Day_Hours"
            set dstintf "wan1"
            set class-id 4
            set srcaddr "all"
            set dstaddr "all"
        next
    end

Allocating bandwidth to the shaping classes

A traffic shaping profile defines the guaranteed and maximum bandwidths each class receives. In this example, file access can use up to 2 Mb/s and web access can use 8 Mb/s from 8:00 AM to 6:00 PM.

To create a traffic shaping profile using the GUI:
  1. Go to Policy & Objects > Traffic Shaping, select the Traffic Shaping Profiles tab, and click Create New.
  2. Enter a name for the profile, such as Day_Hours_Profile.
  3. Configure a default traffic shaping class:

    This class has a high priority, meaning that when the other classes have reached their guaranteed bandwidths, this default class will use the rest of the available bandwidth.

    1. In the Traffic Shaping Classes table click Create New.
    2. Click the Traffic shaping class ID drop down then click Create.
    3. Enter a name for the class, such as Default Access.
    4. Click OK.
    5. Select the class ID you just created for Traffic shaping class ID.
    6. Configure the following settings, then click OK:

      Guaranteed bandwidth

      30

      Maximum bandwidth

      100

      Priority

      High

  4. Configure a web accessing traffic shaping class:

    When other types of traffic are competing for bandwidth, this class is guaranteed to 6 Mb/s, or 60% of the bandwidth.

    1. In the Traffic Shaping Classes table click Create New.
    2. Configure the following settings, then click OK:

      Traffic shaping class ID

      Web Access

      Guaranteed bandwidth

      60

      Maximum bandwidth

      80

      Priority

      Medium

  5. Configure a file accessing traffic shaping class:

    When other types of traffic are competing for bandwidth, this group is guaranteed to 1 Mb/s, or 10% of the bandwidth.

    1. In the Traffic Shaping Classes table click Create New.
    2. Configure the following settings, then click OK:

      Traffic shaping class ID

      File Access

      Guaranteed bandwidth

      10

      Maximum bandwidth

      20

      Priority

      Medium

  6. Click OK.
To create a traffic shaping profile using the CLI:
config firewall shaping-profile
    edit "Day_Hours_Profile"
        set default-class-id 2
        config shaping-entries
            edit 1
                set class-id 2
                set guaranteed-bandwidth-percentage 30
                set maximum-bandwidth-percentage 100
            next
            edit 2
                set class-id 3
                set priority medium
                set guaranteed-bandwidth-percentage 60
                set maximum-bandwidth-percentage 80
            next
            edit 3
                set class-id 4
                set priority medium
                set guaranteed-bandwidth-percentage 10
                set maximum-bandwidth-percentage 20
            next
        end
    next
end

Defining the available bandwidth on an interface

In this example, the link speed of the wan1 interface is 10 Mb/s.

To set the bandwidth of the wan1 interface in the GUI:
  1. Go to Network > Interfaces.
  2. Edit the wan1 interface.
  3. Under Traffic Shaping, enable Outbound shaping profile and select the profile that you just created, Day_Hours_Profile.
  4. Enable Outbound Bandwidth and set it to 10000 Kbps.

  5. Click OK.
To set the bandwidth of the wan1 interface in the CLI:
config system interface
    edit "wan1"
        set egress-shaping-profile "Day_Hours_Profile"
        set outbandwidth 10000
    next
end

Diagnose commands

To check that the specific traffic is put into the correct shaping group or class ID:
# diagnose firewall iprope list 100015
To check the speed limit for each class ID on an interface:
# diagnose netlink interface list wan1

On This Page

Related Videos

sidebar video

Interface Based Traffic Shaping

  • 4,781 views
  • 6 years ago

Interface-based traffic shaping profile

Interface-based traffic shaping profile

A traffic shaping policy can be used for interface-based traffic shaping by organizing traffic into 30 class IDs. The shaping profile defines the percentage of the interface bandwidth that is allocated to each class. Each traffic class ID is shaped to the assigned speed according to the outgoing bandwidth limit configured to the interface.

Traffic classification

A shaping policy classifies traffic and organizes it into different class IDs, based on matching criteria. For traffic matching a criteria, you can choose to put it into 30 different shaping classes, identified by class ID 2 to 31.

You must select an outgoing interface for the traffic. The shaping policy is only applied when the traffic goes to one of the selected outgoing interfaces.

Criterion

Description

Source

  • Address: match the source address of the traffic to the selected address or address group.
  • User: use the user credentials of the traffic to match the selected user or user group. At least one address, address group, or internet service must also be selected.
  • Internet service: match the traffic to the selected internet service. Internet services cannot be used if addresses or address or groups are used.

Destination

  • Address: match the destination address of the traffic to the selected address or address group.
  • Internet service: match the traffic to the selected internet service. Internet services cannot be used if addresses or address or groups are used.

Schedule

Match the current date and time to the selected schedule. You can select a one-time schedule, recurring schedule, or schedule group. This setting is optional.

Service

Match the service of the traffic to the selected service or service group.

Application

Match the application of the traffic to the selected application, application category, or application group.

Application control must be enabled in the related firewall policy to know the application of the traffic. See Application control for more information.

URL category

Match the URL of the traffic to the selected URL category.

Web filter must be enabled in the related firewall policy to know the URL of the traffic. See Web filter for more information.

Note

When multiple items are selected in one criterion, it is considered a match when traffic matches any one of them.

Traffic prioritization

Shaping profiles define how different shaping classes of traffic are prioritized. For each class, you can define three prioritization strategies: guaranteed bandwidth, maximum bandwidth, and priority.

For each shaping profile, a default shaping class must be defined. Traffic is prioritized based on the default shaping group in the following two circumstances:

  • All traffic to the outgoing interface that does not match to any shaping policy
  • Traffic with a shaping group that is not defined in a shaping profile

Prioritization strategy

Description

Guaranteed bandwidth

The percentage of the link speed that is reserved for the shaping group.

The total guaranteed bandwidth for all shaping groups cannot exceed 100%.

Maximum bandwidth

The maximum percentage of the link speed that the shaping group can use.

Priority

The shaping class priority: top, critical, high, medium, or low. When groups are competing for bandwidth on the interface, the group with the higher priority wins.

Applying a shaping profile to an interface

Traffic shaping is accomplished by configuring the outgoing bandwidth and outgoing shaping profile on an interface. The shaping profile uses the outgoing bandwidth of the interface as the maximum link speed, and it only works when the outgoing bandwidth is configured.

This example shows how to apply interface-based traffic shaping to web and file accessing traffic according to a schedule:

  • The link speed of the wan1 interface is 10 Mb/s.
  • File access can use up to 2 Mb/s from 8:00 AM to 6:00 PM.
  • Web access can use 8 Mb/s from 8:00 AM to 6:00 PM.

Putting the traffic into shaping classes

To create a recurring schedule in the GUI:
  1. Go to Policy & Objects > Schedules.
  2. Click Create New > Schedule.
  3. Configure a recurring schedule called Day_Hours for everyday from 8:00 AM to 6:00 PM.
  4. Click OK.
To create a traffic shaping policy and class ID for the web accessing traffic in the GUI:
  1. Go to Policy & Objects > Traffic Shaping, select the Traffic Shaping Policies tab, and click Create New.
  2. Enter a name for the policy, such as web_access_day_hours.
  3. Enable Schedule and select the schedule you just created.
  4. Set Service to web accessing services, such as HTTP and HTTPS.
  5. Set Action to Assign Shaping Class ID, and Outgoing interface to wan1.
  6. Click the Traffic shaping class ID drop down then click Create.
  7. Enter an integer value for the ID (3) and a description for the Name, such as Web Access.
  8. Click OK.
  9. Select the class ID you just created for Traffic shaping class ID.

  10. Configure the remaining settings as required.
  11. Click OK.
To create a traffic shaping policy and class ID for the file accessing traffic in the GUI:
  1. Go to Policy & Objects > Traffic Shaping, select the Traffic Shaping Policies tab, and click Create New.
  2. Enter a name for the policy, such as file_access_day_hours.
  3. Enable Schedule and select the schedule you just created.
  4. Set Service to file accessing services, such as ASF3, FTP and SMB.
  5. Set Action to Assign Shaping Class ID, and Outgoing interface to wan1.
  6. Click the Traffic shaping class ID drop down then click Create.
  7. Enter an integer value for the ID (4) and a description for the Name, such as File Access.
  8. Click OK.
  9. Select the class ID you just created for Traffic shaping class ID.

  10. Configure the remaining settings as required.
  11. Click OK.
To put the traffic into shaping classes in the CLI:
  1. Create a recurring schedule:
    config firewall schedule recurring
        edit "Day_Hours"
            set start 08:00
            set end 18:00
            set day sunday monday tuesday wednesday thursday friday saturday
        next
    end
  2. Create the traffic class IDs:

    config firewall traffic-class
        edit 3
            set class-name "Web Access"
        next
        edit 4
            set class-name "File Access"
        next
    end
  3. Create the web and file accessing traffic shaping policies:
    config firewall shaping-policy
        edit 2
            set name "web_access_day_hours"
            set comment "Limit web accessing traffic to 8Mb/s in day time"
            set service "HTTP" "HTTPS"
            set schedule "Day_Hours"
            set dstintf "wan1"
            set class-id 3
            set srcaddr "all"
            set dstaddr "all"
        next
        edit 3
            set name "file_access_day_hours"
            set comment "Limit file accessing traffic to 2Mb/s during the day"
            set service "AFS3" "FTP" "FTP_GET" "FTP_PUT" "NFS" "SAMBA" "SMB" "TFTP"
            set schedule "Day_Hours"
            set dstintf "wan1"
            set class-id 4
            set srcaddr "all"
            set dstaddr "all"
        next
    end

Allocating bandwidth to the shaping classes

A traffic shaping profile defines the guaranteed and maximum bandwidths each class receives. In this example, file access can use up to 2 Mb/s and web access can use 8 Mb/s from 8:00 AM to 6:00 PM.

To create a traffic shaping profile using the GUI:
  1. Go to Policy & Objects > Traffic Shaping, select the Traffic Shaping Profiles tab, and click Create New.
  2. Enter a name for the profile, such as Day_Hours_Profile.
  3. Configure a default traffic shaping class:

    This class has a high priority, meaning that when the other classes have reached their guaranteed bandwidths, this default class will use the rest of the available bandwidth.

    1. In the Traffic Shaping Classes table click Create New.
    2. Click the Traffic shaping class ID drop down then click Create.
    3. Enter a name for the class, such as Default Access.
    4. Click OK.
    5. Select the class ID you just created for Traffic shaping class ID.
    6. Configure the following settings, then click OK:

      Guaranteed bandwidth

      30

      Maximum bandwidth

      100

      Priority

      High

  4. Configure a web accessing traffic shaping class:

    When other types of traffic are competing for bandwidth, this class is guaranteed to 6 Mb/s, or 60% of the bandwidth.

    1. In the Traffic Shaping Classes table click Create New.
    2. Configure the following settings, then click OK:

      Traffic shaping class ID

      Web Access

      Guaranteed bandwidth

      60

      Maximum bandwidth

      80

      Priority

      Medium

  5. Configure a file accessing traffic shaping class:

    When other types of traffic are competing for bandwidth, this group is guaranteed to 1 Mb/s, or 10% of the bandwidth.

    1. In the Traffic Shaping Classes table click Create New.
    2. Configure the following settings, then click OK:

      Traffic shaping class ID

      File Access

      Guaranteed bandwidth

      10

      Maximum bandwidth

      20

      Priority

      Medium

  6. Click OK.
To create a traffic shaping profile using the CLI:
config firewall shaping-profile
    edit "Day_Hours_Profile"
        set default-class-id 2
        config shaping-entries
            edit 1
                set class-id 2
                set guaranteed-bandwidth-percentage 30
                set maximum-bandwidth-percentage 100
            next
            edit 2
                set class-id 3
                set priority medium
                set guaranteed-bandwidth-percentage 60
                set maximum-bandwidth-percentage 80
            next
            edit 3
                set class-id 4
                set priority medium
                set guaranteed-bandwidth-percentage 10
                set maximum-bandwidth-percentage 20
            next
        end
    next
end

Defining the available bandwidth on an interface

In this example, the link speed of the wan1 interface is 10 Mb/s.

To set the bandwidth of the wan1 interface in the GUI:
  1. Go to Network > Interfaces.
  2. Edit the wan1 interface.
  3. Under Traffic Shaping, enable Outbound shaping profile and select the profile that you just created, Day_Hours_Profile.
  4. Enable Outbound Bandwidth and set it to 10000 Kbps.

  5. Click OK.
To set the bandwidth of the wan1 interface in the CLI:
config system interface
    edit "wan1"
        set egress-shaping-profile "Day_Hours_Profile"
        set outbandwidth 10000
    next
end

Diagnose commands

To check that the specific traffic is put into the correct shaping group or class ID:
# diagnose firewall iprope list 100015
To check the speed limit for each class ID on an interface:
# diagnose netlink interface list wan1