Fortinet black logo

FortiSIEM Sizing Guide

FortiSIEM Sizing Guide

This document provides information about the following topics:

Minimum Requirements

Browser Display

FortiSIEM, like most monitoring, SIEM and analytics tools, shows a lot of information on the screen at once. FortiSIEM HTML GUI has chosen a bigger font for legibility reasons. Hence, Fortinet recommends that users have a minimum 1680x1050 desktop display resolution.

Hardware

Minimum hardware requirements for FortiSIEM nodes are as follows.

Node vCPU RAM Local Disks
Supervisor (All in one) Minimum – 12
Recommended - 32

Minimum

  • without UEBA – 24GB
  • with UEBA - 32GB

Recommended

  • without UEBA – 32GB
  • with UEBA - 64GB

OS – 25GB

OPT – 100GB

CMDB – 60GB

SVN – 60GB

Local Event database – based on need

Supervisor (Cluster) Minimum – 12
Recommended - 32

Minimum

  • without UEBA – 24GB
  • with UEBA - 32GB

Recommended

  • without UEBA – 32GB
  • with UEBA - 64GB

OS – 25GB

OPT – 100GB

CMDB – 60GB

SVN – 60GB

Workers Minimum – 8
Recommended - 16

Minimum – 16GB

Recommended
  • without UEBA – 24GB
  • with UEBA - 32GB

OS – 25GB

OPT – 100GB

Collector Minimum – 4
Recommended – 8 ( based on load)

Minimum – 4GB

Recommended – 8GB

OS – 25GB

OPT – 100GB

  • Supervisor VA needs more memory since it hosts many heavy-duty components such as Application Server (Java), PostGreSQL Database Server and Rule Master.
  • With Elasticsearch, Supervisor VA also hosts the Java Query Server component for communicating with Elasticsearch – hence the need for additional 8 GB memory.
  • For OPT - 100GB, the 100GB disk for /opt will consist of a single disk that will split into 2 partitions, /OPT and swap. The partitions will be created and managed by FortiSIEM when configFSM.sh runs.

Note that these are only the minimum requirements. The performance may improve by increasing vCPUs and RAM in certain situations. External storage depends on your EPS mix and the number of days of log storage needs. To provide more meaningful guidance, scalability tests were conducted as described below.

Internal Scalability Tests

FortiSIEM team performed several scalability tests described below.

Test Setup

  • A specific set of events were sent repeatedly to achieve the target EPS.
  • The target EPS was constant over time.
  • A set of Linux servers were monitored via SNMP and performance monitoring data was collected.
  • Events triggered many incidents.

Test Success Criteria

The following success criteria should be met on testing:

  • Incoming EPS must be sustained without any event loss.
  • Summary dashboards should be up to date and not fall behind.
  • Widget dashboards should show data indicating that inline reporting is keeping up.
  • Incidents should be up to date.
  • Real-time search should show current data and trend chart should reflect incoming EPS.
  • GUI navigation should be smooth.
  • CPU, memory and IOPS are not maxed out. Load average must be less than the number of cores.

The tests were run for three cases:

  • All-in-one FSM Hardware Appliance: FSM-2000F and FSM-3500F with collectors FSM-500F sending events.
  • FSM Virtual Appliance with FortiSIEM EventDB as the data store.
  • FSM Virtual Appliance with Elasticsearch as the data store.

Hardware Appliance EPS Test with FortiSIEM Event Database

The test beds is shown below. Scripts generated events on FSM-500F Collectors, which parsed those events and sent them to the appliances.


The results are shown below:

Event Sender
FortiSIEM HW ApplianceHardware Spec

Collector Model

CountEPS/CollectorSustained EPS without Loss
FSM-2000F2000F - 12vCPU (1x6C2T), 32GB RAM, 12x3TB SATA (3 RAID Groups)FSM-500F35K15K
FSM-2000G2000G - 40vCPU(2x10C2T), 128GB RAM, 4x1TB SSD (RAID5), 8x4TB SAS (2 RAID50 Groups) FSM-500F36K20K

FSM-3500G

3500G,48vCPU(2x12C2T),128GB RAM,24x4TBSATA (3 RAID50 groups)FSM-500F

6

8K

40K

Hardware Appliance EPS Test with ClickHouse

The test bed is shown below. Scripts generated events on FSM-500F Collectors, which parsed those events and sent to the appliances.

Event Sender
FortiSIEM HW Appliance Hardware Spec

Collector Model

Count EPS/Collector Sustained EPS without Loss
FSM-2000F 2000F - 12vCPU (1x6C2T), 32GB RAM, 12x3TB SATA (3 RAID Groups)

FSM-500F

3 5K 15K
FSM-2000G 2000G - 40vCPU(2x10C2T), 128GB RAM, 4x1TB SSD (RAID5), 8x4TB SAS (2 RAID50 Groups)

FSM-500F

6 6K 40K

FSM-3500G

3500G,48vCPU(2x12C2T),128GB RAM,24x4TBSATA (3 RAID50 groups)

FSM-500F

6

8K

40K

Notes:

  1. For FSM-2000G, event ingestion speed increased two fold with ClickHouse compared to FortiSIEM EventDB. ClickHouse event database made better utilization of the vCPUs in the system.

  2. Since FSM-2000F has fewer vCPU compared to FSM-2000G, the performance of both FortiSIEM EventDB and ClickHouse are identical. The appliance is CPU bound.

  3. For FortiSIEM 3500G, the insert performance of FortiSIEM EventDB and ClickHouse are identical as FortiSIEM EventDB could also use disk striping for better I/O.

Virtual Appliance EPS Test with FortiSIEM Event Database

All tests were done in AWS. The following hardware was used.

Type AWS Instance Type Hardware Spec
Collector c4.xlarge 4vCPU, 7 GB RAM
Worker c4.2xlarge 8vCPU, 15 GB RAM
Super m4.4xlarge 16vCPU, 64 GB RAM, CMDB Disk 10K IOPS
NFS Server c4.2xlarge 8vCPU, 16 GB RAM, 10K IOPS

The test bed is as follows:

The following result shows 10K EPS sustained per Worker with over 20K CMDB Devices.

Event Sender Event Handler
Collector Count EPS/Collector Monitored Device/Collector Super Workers Orgs CMDB Device Sustained EPS without Loss
150 200 150 1 3 150 22,500 30K

Virtual Appliance EPS Test with Elasticsearch Database

All tests were done in AWS. The following hardware was used.

Type AWS Instance Type Hardware Spec
Collector c4.xlarge 4vCPU, 7 GB RAM
Worker c4.2xlarge 8vCPU, 15 GB RAM
Super m4.4xlarge 16vCPU, 64 GB RAM, CMDB Disk 10K IOPS
Elastic Search Master Node c3.2xlarge 8vCPU, 16 GB RAM with 8 GB JVM
Elastic Search Coordinating Node m5.4xlarge 16vCPU, 64 GB RAM with 30 GB JVM allocation
Elastic Search Data Node i3.4xlarge 16vCPU, 122 GB RAM, 1.9TBx2 NVMe SSD Instance-store Volumes, 30 GB JVM

The test bed was as follows:

The following result shows 5K EPS sustained per Data Node with over 20K CMDB Devices.

Event Sender Event Handler
Collector Count EPS/ Collector Monitored Device/ Collector Super Workers Elastic (M/CO/DN/ Shards)* Orgs CMDB Device Sustained EPS without Loss
150 200 150 1 3 1/1/5/10 150 22,500 30K
* M = Elasticsearch Master, CO = Elasticsearch Co-ordinator, DN = Elasticsearch Data Node

Sizing Online Deployments

EventDB based deployment, Elasticsearch, and ClickHouse based deployments are available.

EventDB Based Deployment

Processing Requirement

Requirement Recommendation
EPS Deployment HW Model SW Configuration
Nodes HW Per Node (vCPU, RAM) NFS IOPS
Up to 5K Hardware FSM-2000F
Up to 5K Software All-in-one 16, 24GB
5K – 10K Hardware FSM-2000F
5K – 10K Software Supervisor 16, 24GB
1 Worker 8, 16GB 2000
10K – 15K Hardware FSM-3500F
10K – 15K Software Supervisor 16, 24GB
2 Workers 8, 16GB 3000
15K – 25K Hardware FSM-3500F
15K – 25K Software Supervisor 16, 24GB
3 Workers 16,16GB 5000
25K – 35K Software Supervisor 16, 24GB
4 Workers 16, 16GB 7000
Add 10K EPS Software Add 1 Worker 16, 16GB Add 2000 IOPS
10K – 15K Hardware FSM-3500G
10K – 15K Software Supervisor 16, 24GB
2 Workers 8, 16GB 3000
15K – 25K Hardware FSM-3500G
15K – 25K Software Supervisor 16, 24GB
3 Workers 16, 16GB 5000
25K – 35K Software Supervisor 16, 24GB
4 Workers 16, 16GB 7000
Add 10K EPS Software Add 1 Worker 16, 16GB Add 2000 IOPS

Storage Requirement for FortiSIEM EventDB

FortiSIEM storage requirement depends on three factors:

  • EPS
  • Bytes/log mix in your environment
  • Compression ratio (8:1)

You are likely licensed for Peak EPS. Typically, EPS peaks during morning hours on weekdays and goes down dramatically after 2 pm on weekdays and also remains low on weekends. So the average EPS should be used to calculate storage needs.

For calculating Bytes/log, consider the following aspects:

  • Network devices and Linux servers tend to send shorter logs (150-200 bytes/log) while Windows Security logs tend to be much larger (500-1000 bytes/log).
  • Busy corporate firewalls and domain controllers tend to send much higher log volumes (higher EPS) than other systems, assuming they are sending all logs.
  • Database indices built on logs for efficient searching consumes significant storage as well.
  • ASCII text (syslog) compresses much better than binary (for example, Netflow)

Therefore, it is difficult to properly assume a specific bytes/log mix in your environment without measurement. Our experience from sampling of 5 large customers has shown that Bytes/log is between 100-150 including all factors – device mix, log mix, indexing cost and compression. Fortinet calculated this by dividing the total FortiSIEM event file size (in \data) over one day by the total number of events on that day, and then averaging over a few days.

It is important to provision the NFS server with enough IOPS and network bandwidth for read and write of event data and where possible cater for peaks in EPS. It is recommended that NFS is provisioned with 10Gbit interfaces or higher and the FortiSIEM Supervisor and Worker nodes to also be provisioned with 10Gbit interfaces to the NFS storage network.

The table below shows two scenarios – Worst case and average case for NFS storage. In worst case, Peak EPS and 150 Bytes/log is used. In the average case, 0.5 Peak EPS and 100 Bytes/log is used.

Peak EPS

Storage (Months)

NFS Storage (TB)*

Worst Case Average Case
1000 12 5 1.66
1000 24 9 3
1000 36 14 4.66
2000 12 9 3
2000 24 19 6.33
2000 36 28 9.33
5000 12 23 7.66
5000 24 47 15.66
5000 36 70 23.33
10000 12 47 15.66
10000 24 93 31
10000 36 140 46.66

NFS Storage (TB):

  • Worst case = (Peak EPS*150*86400*30*Storage(Months))/10^12
  • Average case = (0.5*Peak EPS*100*86400*30*Storage(Months))/10^12

Elasticsearch Based Deployment

This section provides information about the following Elasticsearch based deployment topics:

Background

An Elasticsearch deployment consists of

  • Master node (required)

  • Coordinator Only nodes (required)

  • Data nodes – Hot, Warm and Frozen (See below)

Keep the following points in mind about Hot, Warm and Frozen Data nodes:

  • FortiSIEM inserts events into Hot nodes, so Hot nodes need fast disk I/O to handle inserts and reads. A solid state drive (SSD) with more than 200Gb/s I/O throughput are recommended for hot nodes.

  • User can specify Hot node retention policy (days) in FortiSIEM. When this limit is reached, or Hot node disk usage reaches its high watermark (75% full), events are moved from Hot nodes to Warm nodes, to make room for new events in the Hot node. Warm nodes only handle event reads, so they can afford slightly lower speed disks than Hot nodes. Hard disk drives or DAS/SAN disks with about 100 Gb/s I/O throughput are recommended. Warm nodes will have similar query response times as Hot nodes, as they aren’t performing expensive indexing operations.

  • User can specify Warm node retention policy (days) in FortiSIEM. When this limit is reached, or Warm node disk usage reaches its high watermark (75% full), events are moved from Warm nodes to Frozen nodes. In the Frozen nodes, indices are flushed from memory to disk, so Frozen nodes can have much larger disks. Fortinet recommends Frozen nodes to have similar disk speeds as Warm nodes, but with larger capacity. When a user queries for data in Frozen nodes, the Frozen nodes will temporarily rehydrate the required indices to memory, and then flush to disk after the query is complete. Therefore, Frozen nodes will have higher query response time.

When using Elasticsearch in FortiSIEM, hot nodes are the minimum requirement. A budget friendly way to add additional storage is to add Warm nodes. For even more capacity, Frozen nodes can be added.

While Elasticsearch Frozen nodes can provide some Archive options, FortiSIEM provides two additional Archive options with higher compression – FortiSIEM EventDB on NFS and HDFS. Should you choose to use archiving, ensure you use the Real Time Archive option so that events are written to the Archive at the point of insertion into Hot nodes. This eliminates the need for moving data from Online to Archive, as it is prohibitively expensive to read events out of Elasticsearch and write back to Archive.

To summarize, the following options are available for Elasticsearch:

  • Online

    • Elasticsearch

      • Hot node only

      • Hot node and Warm node

      • Hot node, Warm node, and Frozen node

  • Archive

    • EventDB on NFS

    • HDFS

FortiSIEM has a dynamic shard management feature to keep Elasticsearch working optimally.

  • For Hot nodes, FortiSIEM lets a shard grow up to 40GB (Elasticsearch limit 50GB), and closes it once the 40GB limit is reached. In a low EPS situation, a shard can span multiple days. FortiSIEM uses an aliasing technique to string the shards together. In a high EPS situation, there can be multiple shards in a day.

  • Segment merge is performed to reduce heap usage for indices older than 2 days.

Recommended Elasticsearch Configuration

Fortinet recommends the following configuration steps.

  • Replica – at least 1

  • Master, Coordinator Only nodes and Data nodes on different machines

  • 3 Master nodes – each with 8 vCPU, 16 GB RAM

  • At least 2 Coordinator Only nodes – each with 16 vCPU, 32 GB RAM. Two Coordinator Only nodes are chosen for failover. The exact number of Coordinator Only nodes depends on the EPS. See below for details.

  • At least 3 Hot Data nodes – each with 32 vCPU, 64GB RAM and SSD disks with at least 200 Gb/s I/O throughput. The exact number of Hot Data nodes depends on the EPS and retention policy (see below).

  • If you decide to deploy Warm nodes, deploy at least 3 Warm Data nodes – each with 32 vCPU, 64GB RAM and disks with at least 100 Gb/s I/O throughput. The exact number of Warm Data nodes depends on retention policy (see below).

  • If you decide to deploy Frozen nodes, deploy at least 3 Frozen Data nodes – each with 16 vCPU, 64GB RAM and around 100 Gb/s I/O throughput. The exact number of Frozen Data nodes depends on retention policy (see below).

  • If you decide to utilize the Archive option, then choose the Real Time Archive option.

  • Enable FortiSIEM dynamic shard management feature (Under Shard Allocation, select Dynamic).

  • Do not choose Per Org Index unless you have to. Keeping a separate index per organization enables you to efficiently delete an organization’s data, but increases the shard count, which in turn requires more nodes because of the 500 shards per node limit.

  • Follow the Pre-install considerations in the setup guide.

Sizing of Coordinator Only Nodes

Our testing has shown that 1 Coordinator Only node with 16 vCPU and 64 GB RAM (32 GB to Elasticsearch and the rest to the operating system) can handle 200K EPS. So choose the number of Coordinator Only nodes based on your EPS and keep one extra in case a Coordinator Only node dies.

Peak EPS Coordinator Only Nodes (16 vCPU and 64 GB RAM)
50K 2
100K 2
200K 3
500K 4
1 Million 6

Sizing of Hot Data Nodes

Choose each Hot Data node to have 32 vCPU, 64GB RAM (32 GB to Elasticsearch and the rest to the operating system), and SSD with at least 200Gbps I/O throughput. Use the calculations below to find the exact number of Hot nodes. This depends on the EPS and the retention policy.

Assumptions
  • Our experiments have shown that FortiSIEM can insert 60K EPS per Data node without Replica and without any loss

  • Measurements from various SIEM installs have shown that Elasticsearch consumes an average of 500 bytes to store an event and all its parsed attributes

  • Memory to Disk Ratio = 1:30. See the Elasticsearch reference documents in References.

  • Max 75% disk capacity for storing event indices since Elasticsearch will use the rest of the 25%. See the Elasticsearch reference documents in References.

Storage per Day

Suppose

  • R: Number of Replica (at least 1 is recommended)

  • E: EPS

  • D: Retention (days) in Hot nodes

Data per day = E * #seconds in a day (86400) * 500 Bytes * (R +1)

Storage per day = 1.25 * Data per day

# Hot Data Nodes from Elasticsearch Constraint

Min # Hot Data nodes = Storage per day * D / RAM / 30

# Hot Data Nodes from EPS Constraint

Suppose

  • R: Number of Replica (at least 1 is recommended)

  • E: EPS

Since FortiSIEM can insert 60K EPS without Replica and without any loss,

Min # Hot Data nodes = E * (R+1) / 60K

Cluster Wide Shard Count Limit

In Elasticsearch 6.x, Fortinet has observed that Elasticsearch CLI performance degrades when the total number of shards in the cluster (including Hot and Warm nodes) is more than 15K. Newer versions may have a higher upper limit.

You can calculate the number of shards as follows.

  • Node Count: N

  • Disk Size on each node: D TB

Assuming 40GB per shard, the total number of shards = (N * D TB) / 40GB

For example, at 50K EPS: (consult the two tables below)

  • Hot Node: 7 days retention, number of shards = (19*2TB) / 40GB = 950

  • Warm Node: 30 days retention, number of shards = (15*10TB) / 40GB = 3750

  • Total shards in the cluster = 4700

As you map out higher EPS and longer days, make sure the total number of shards stays within the limit.

Examples

Here are some representative numbers for Replica = 1

EPS Storage per Day Retention (Days) Hot Data Nodes
(32vCPU, 64GB RAM, SSD)

Node Count Disk Size
10K 1TB 7 4 2TB
30 16 2TB
50K 5TB 7 19 2TB
14 38 2TB
30 80 2TB
100K 10TB 7 38 2TB
14 76 2TB
30 160 2TB
200K 20TB 7 76 2TB
14 152 2TB
500K 50TB 7 190 2TB
14 380 2TB
1 Million 100TB 7 380 2TB
14 760 2TB

Sizing of Warm Data Nodes

Warm nodes are configured identically as Hot Data nodes, except that memory to disk ratio = 1:160. Make sure you have 32vCPU, 64GB RAM to host with 32 GB to Elasticsearch and 32GB to the operating system. See the Elasticsearch reference documents in References.

Min # Warm Data nodes = Storage per day * D / RAM / 160

Examples

Here are some representative numbers for Replica = 1

EPS Storage per Day Retention (Days) Warm Data Nodes
(32vCPU, 64GB RAM and ~100Gbps Disk I/O)
Node Count Disk Size
10K 1TB 30 3 10TB
60 6 10TB
90 9 10TB
50K 5TB 30 15 10TB
60 30 10TB
90 45 10TB
100K 10TB 30 30 10TB
60 60 10TB
200K 20TB 30 60 10TB
60 120 10TB
500K 50TB 30 150 10TB
60 300 10TB
1 Million 100TB 30 300 10TB
60 600 10TB

Sizing of Frozen Data Nodes

Frozen nodes are configured identically as Warm or Hot Data nodes, except for a higher memory to disk ratio = 1:1000. Note that the required query latency, rather than system resources, often limits the amount of data stored on Frozen nodes. See the Elasticsearch reference documents in References.

Frozen nodes behave identically except for memory to disk ratio = 1:1000

Min # Frozen Data nodes = Storage per day * D / RAM / 1000

Examples

Here are some representative numbers for Replica = 1

EPS Storage per Day Retention (Days) Frozen Data Nodes
(16vCPU, 64GB RAM, HDD <100Gbps)

Node Count Disk Size
10K 1TB 90 2 60TB
180 4 60TB

365 7 60TB
50K 5TB 90 8 60TB
180 16 60TB
365 32 60TB
100K 10TB 90 15 60TB
180 30 60TB

365 60 60TB
200K 20TB 90 30 60TB
180 60 60TB

365 120 60TB
500K 50TB 90 75 60TB
180 150 60TB
365 300 60TB
1 Million 100TB 90 150 60TB
180 300 60TB
365 600 60TB

ClickHouse Based Deployment

Processing Requirement

EPS

Nodes

HW per Node (vCPU, RAM)

Disk Type

Up to 5K All-in-one 16, 24GB 2 tier (SSD,SAS) with RAID recommended but not required - see FSM-2000G hardware spec. If you use one tier then SAS disks are preferred.
5K - 10K All-in-one 24, 32GB 2 tier (SSD,SAS) with RAID recommended but not required - see FSM-2000G hardware spec. If you use one tier then SAS disks are preferred.
10K - 15K All-in-one 32, 48GB 2 tier (SSD,SAS) with RAID recommended but not required - see FSM-2000G hardware spec. If you use one tier then SAS disks are preferred.
15K - 40K All-in-one 48, 64GB 2 tier (SSD,SAS) with RAID required - see FSM-2000G hardware spec

See ClickHouse Usage Recommendations in References for more information.

Storage Requirement for ClickHouse

ClickHouse Storage requirement is the same as FortiSIEM EventDB. Consult that section for calculating storage sizes for your environment. If you choose 2 tier storage, then the size of the SSD can be chosen based on budget and number of days for which very fast query response is required.

Sizing Archive Deployments

FortiSIEM Event Archives can be based on FortiSIEM EventDB on NFS or HDFS.

FortiSIEM EventDB Based Deployments

In this situation, online workers are used to query the Archived EventDB database, so only a NFS infrastructure is required. Since Archived data is not indexed, our experiments have shown that Archived EventDB needs about 60% storage compared to Online EventDB. This information can be used to estimate the amount of NFS storage required for Archive.

EPS Retention NFS Storage
Worst Case (100 Bytes/log) Average Case (66 Bytes/log)
5K 6 months 7.5 TB 2.5 TB
1 year 15 TB 5 TB
3 years 45 TB 15 TB
10K 6 months 15 TB 5 TB
1 year 30 TB 10 TB
3 years 90 TB 30 TB
20K 6 months 30 TB 10 TB
1 year 60 TB 20 TB
3 years 180 TB 60 TB
50K 6 months 75 TB 25 TB
1 year 150 TB 50 TB
3 years 450 TB 150 TB
100K 6 months 150 TB 50 TB
1 year 300 TB 100 TB

3 years 900 TB 100 TB

Worst Case Storage = EPS * 86400 * worst case bytes/log * retention

Average Case Storage = 0.5* EPS * 86400 * average case bytes/log * retention

Used 1024 for B -> KB etc.

HDFS Based Deployments

An HDFS based deployment needs the following:

  • Name node

  • Spark Master node

  • Spark Slave node

  • Data node

According to HDFS best practices, the following co-locations are possible:

  • Node Type A containing Name node – need 2 of these – 8vCPU and 16GB RAM each

  • Node Type B containing Spark Master and Slave node – need 2 of these - – 8vCPU and 16GB RAM each

  • Node Type C containing Slave node and Data node – need N of these based on insert and query requirements.

Our experiments have shown that

  • HDFS Parquet file system uses 125 bytes/event (25% of Elasticsearch storage and 30% more than FortiSIEM EventDB).

  • HDFS can insert events at 200K EPS per Data node, so insert speed is not a determining criteria.

Spark / HDFS Resource Allocation Considerations

Spark / HDFS can run the following 4 jobs.

  1. Real time Archive job

  2. Non-real time Archive job

  3. Query Job from Supervisor

  4. Merge job to merge small files written to HDFS into bigger files

The resource allocation strategy is as follows:

totalCore = Total number of cores on Spark Worker nodes

totalWorker = Total number of Spark Worker nodes

availCore = (totalCore-totalWorker) available to the 4 job types above

nodeCore = Total number of cores on one single Spark worker node

Strategy
  1. Real time archive job is allocated rm_lambda_percent (default 30) of resources. This parameter is defined in /home/admin/FortiSIEM/config.txt.

  2. Remaining resources are allocated to 3 other job types in an equal manner. The parameter rm_max_concurrent_jobs (default 5) defined in /home/admin/FortiSIEM/config.txt defines the maximum number of such jobs. Each executor needs to be allocated 5 cores to run, Hence the maximum value of rm_max_concurrent_jobs should be the minimum value of the following two calculations:

    1. (availCore * ((100 - rm_lambda_percent) / 100)) / 5.

    2. (nodeCore - 1) * ((100 - rm_lambda_percent) / 100) / 5 * totalWorker

These two calculations may differ as the lower integer needs to be retrieved when dividing by 5.

Example

10 Spark nodes each 16 core and 32GB RAM.

totalCore = 160

totalWorker = 10

availCore = 150

rm_lambda_percent = 30

rm_max_concurrent_job = 20

  1. Real time archive job will be assigned with at most 9 executors, each with 5 core and 10GB RAM. Spark will dynamically adjust the executor numbers based on running status.

  2. A resource pool of 20 jobs are created, each with 5 core and 10GB RAM. Each of these can run the other 3 jobs based on demand.


Based on this, the following sizing is suggested.

EPS

Storage per Day

(Replica = 1)

Retention

Total Storage

Spark Slave + Data Node

(16 vCPU, 32GB RAM, HDD – 100 Gbps)

Count Disk Storage
10K 125 GB 1 year 45 TB 6 8 TB
3 years 134 TB 6 24 TB
50K 625 GB 1 year 225 TB 10 24 TB
3 years 675 TB 10 80 TB
100K 1.25 TB 1 year 460 TB 10 48 TB
3 years 1,380 TB 10 160 TB
200K 2.5 TB 1 year 920 TB 10 96 TB
3 years 2,760 TB 10 300 TB
500K 5.75 TB 1 year 2,250 TB 8 300 TB
3 years 6,750 TB 25 300 TB
1 Million 11.5 TB 1 year 4,450 TB 15 300 TB
3 years 13,350 TB 25 600 TB

References

Elasticsearch Concepts and Sizing Guide

https://www.elastic.co/pdf/elasticsearch-sizing-and-capacity-planning.pdf

Elasticsearch Sizing Guide

https://www.elastic.co/blog/benchmarking-and-sizing-your-elasticsearch-cluster-for-logs-and-metrics

ClickHouse Usage Recommendations

https://clickhouse.com/docs/en/operations/tips/

FortiSIEM Sizing Guide

This document provides information about the following topics:

Minimum Requirements

Browser Display

FortiSIEM, like most monitoring, SIEM and analytics tools, shows a lot of information on the screen at once. FortiSIEM HTML GUI has chosen a bigger font for legibility reasons. Hence, Fortinet recommends that users have a minimum 1680x1050 desktop display resolution.

Hardware

Minimum hardware requirements for FortiSIEM nodes are as follows.

Node vCPU RAM Local Disks
Supervisor (All in one) Minimum – 12
Recommended - 32

Minimum

  • without UEBA – 24GB
  • with UEBA - 32GB

Recommended

  • without UEBA – 32GB
  • with UEBA - 64GB

OS – 25GB

OPT – 100GB

CMDB – 60GB

SVN – 60GB

Local Event database – based on need

Supervisor (Cluster) Minimum – 12
Recommended - 32

Minimum

  • without UEBA – 24GB
  • with UEBA - 32GB

Recommended

  • without UEBA – 32GB
  • with UEBA - 64GB

OS – 25GB

OPT – 100GB

CMDB – 60GB

SVN – 60GB

Workers Minimum – 8
Recommended - 16

Minimum – 16GB

Recommended
  • without UEBA – 24GB
  • with UEBA - 32GB

OS – 25GB

OPT – 100GB

Collector Minimum – 4
Recommended – 8 ( based on load)

Minimum – 4GB

Recommended – 8GB

OS – 25GB

OPT – 100GB

  • Supervisor VA needs more memory since it hosts many heavy-duty components such as Application Server (Java), PostGreSQL Database Server and Rule Master.
  • With Elasticsearch, Supervisor VA also hosts the Java Query Server component for communicating with Elasticsearch – hence the need for additional 8 GB memory.
  • For OPT - 100GB, the 100GB disk for /opt will consist of a single disk that will split into 2 partitions, /OPT and swap. The partitions will be created and managed by FortiSIEM when configFSM.sh runs.

Note that these are only the minimum requirements. The performance may improve by increasing vCPUs and RAM in certain situations. External storage depends on your EPS mix and the number of days of log storage needs. To provide more meaningful guidance, scalability tests were conducted as described below.

Internal Scalability Tests

FortiSIEM team performed several scalability tests described below.

Test Setup

  • A specific set of events were sent repeatedly to achieve the target EPS.
  • The target EPS was constant over time.
  • A set of Linux servers were monitored via SNMP and performance monitoring data was collected.
  • Events triggered many incidents.

Test Success Criteria

The following success criteria should be met on testing:

  • Incoming EPS must be sustained without any event loss.
  • Summary dashboards should be up to date and not fall behind.
  • Widget dashboards should show data indicating that inline reporting is keeping up.
  • Incidents should be up to date.
  • Real-time search should show current data and trend chart should reflect incoming EPS.
  • GUI navigation should be smooth.
  • CPU, memory and IOPS are not maxed out. Load average must be less than the number of cores.

The tests were run for three cases:

  • All-in-one FSM Hardware Appliance: FSM-2000F and FSM-3500F with collectors FSM-500F sending events.
  • FSM Virtual Appliance with FortiSIEM EventDB as the data store.
  • FSM Virtual Appliance with Elasticsearch as the data store.

Hardware Appliance EPS Test with FortiSIEM Event Database

The test beds is shown below. Scripts generated events on FSM-500F Collectors, which parsed those events and sent them to the appliances.


The results are shown below:

Event Sender
FortiSIEM HW ApplianceHardware Spec

Collector Model

CountEPS/CollectorSustained EPS without Loss
FSM-2000F2000F - 12vCPU (1x6C2T), 32GB RAM, 12x3TB SATA (3 RAID Groups)FSM-500F35K15K
FSM-2000G2000G - 40vCPU(2x10C2T), 128GB RAM, 4x1TB SSD (RAID5), 8x4TB SAS (2 RAID50 Groups) FSM-500F36K20K

FSM-3500G

3500G,48vCPU(2x12C2T),128GB RAM,24x4TBSATA (3 RAID50 groups)FSM-500F

6

8K

40K

Hardware Appliance EPS Test with ClickHouse

The test bed is shown below. Scripts generated events on FSM-500F Collectors, which parsed those events and sent to the appliances.

Event Sender
FortiSIEM HW Appliance Hardware Spec

Collector Model

Count EPS/Collector Sustained EPS without Loss
FSM-2000F 2000F - 12vCPU (1x6C2T), 32GB RAM, 12x3TB SATA (3 RAID Groups)

FSM-500F

3 5K 15K
FSM-2000G 2000G - 40vCPU(2x10C2T), 128GB RAM, 4x1TB SSD (RAID5), 8x4TB SAS (2 RAID50 Groups)

FSM-500F

6 6K 40K

FSM-3500G

3500G,48vCPU(2x12C2T),128GB RAM,24x4TBSATA (3 RAID50 groups)

FSM-500F

6

8K

40K

Notes:

  1. For FSM-2000G, event ingestion speed increased two fold with ClickHouse compared to FortiSIEM EventDB. ClickHouse event database made better utilization of the vCPUs in the system.

  2. Since FSM-2000F has fewer vCPU compared to FSM-2000G, the performance of both FortiSIEM EventDB and ClickHouse are identical. The appliance is CPU bound.

  3. For FortiSIEM 3500G, the insert performance of FortiSIEM EventDB and ClickHouse are identical as FortiSIEM EventDB could also use disk striping for better I/O.

Virtual Appliance EPS Test with FortiSIEM Event Database

All tests were done in AWS. The following hardware was used.

Type AWS Instance Type Hardware Spec
Collector c4.xlarge 4vCPU, 7 GB RAM
Worker c4.2xlarge 8vCPU, 15 GB RAM
Super m4.4xlarge 16vCPU, 64 GB RAM, CMDB Disk 10K IOPS
NFS Server c4.2xlarge 8vCPU, 16 GB RAM, 10K IOPS

The test bed is as follows:

The following result shows 10K EPS sustained per Worker with over 20K CMDB Devices.

Event Sender Event Handler
Collector Count EPS/Collector Monitored Device/Collector Super Workers Orgs CMDB Device Sustained EPS without Loss
150 200 150 1 3 150 22,500 30K

Virtual Appliance EPS Test with Elasticsearch Database

All tests were done in AWS. The following hardware was used.

Type AWS Instance Type Hardware Spec
Collector c4.xlarge 4vCPU, 7 GB RAM
Worker c4.2xlarge 8vCPU, 15 GB RAM
Super m4.4xlarge 16vCPU, 64 GB RAM, CMDB Disk 10K IOPS
Elastic Search Master Node c3.2xlarge 8vCPU, 16 GB RAM with 8 GB JVM
Elastic Search Coordinating Node m5.4xlarge 16vCPU, 64 GB RAM with 30 GB JVM allocation
Elastic Search Data Node i3.4xlarge 16vCPU, 122 GB RAM, 1.9TBx2 NVMe SSD Instance-store Volumes, 30 GB JVM

The test bed was as follows:

The following result shows 5K EPS sustained per Data Node with over 20K CMDB Devices.

Event Sender Event Handler
Collector Count EPS/ Collector Monitored Device/ Collector Super Workers Elastic (M/CO/DN/ Shards)* Orgs CMDB Device Sustained EPS without Loss
150 200 150 1 3 1/1/5/10 150 22,500 30K
* M = Elasticsearch Master, CO = Elasticsearch Co-ordinator, DN = Elasticsearch Data Node

Sizing Online Deployments

EventDB based deployment, Elasticsearch, and ClickHouse based deployments are available.

EventDB Based Deployment

Processing Requirement

Requirement Recommendation
EPS Deployment HW Model SW Configuration
Nodes HW Per Node (vCPU, RAM) NFS IOPS
Up to 5K Hardware FSM-2000F
Up to 5K Software All-in-one 16, 24GB
5K – 10K Hardware FSM-2000F
5K – 10K Software Supervisor 16, 24GB
1 Worker 8, 16GB 2000
10K – 15K Hardware FSM-3500F
10K – 15K Software Supervisor 16, 24GB
2 Workers 8, 16GB 3000
15K – 25K Hardware FSM-3500F
15K – 25K Software Supervisor 16, 24GB
3 Workers 16,16GB 5000
25K – 35K Software Supervisor 16, 24GB
4 Workers 16, 16GB 7000
Add 10K EPS Software Add 1 Worker 16, 16GB Add 2000 IOPS
10K – 15K Hardware FSM-3500G
10K – 15K Software Supervisor 16, 24GB
2 Workers 8, 16GB 3000
15K – 25K Hardware FSM-3500G
15K – 25K Software Supervisor 16, 24GB
3 Workers 16, 16GB 5000
25K – 35K Software Supervisor 16, 24GB
4 Workers 16, 16GB 7000
Add 10K EPS Software Add 1 Worker 16, 16GB Add 2000 IOPS

Storage Requirement for FortiSIEM EventDB

FortiSIEM storage requirement depends on three factors:

  • EPS
  • Bytes/log mix in your environment
  • Compression ratio (8:1)

You are likely licensed for Peak EPS. Typically, EPS peaks during morning hours on weekdays and goes down dramatically after 2 pm on weekdays and also remains low on weekends. So the average EPS should be used to calculate storage needs.

For calculating Bytes/log, consider the following aspects:

  • Network devices and Linux servers tend to send shorter logs (150-200 bytes/log) while Windows Security logs tend to be much larger (500-1000 bytes/log).
  • Busy corporate firewalls and domain controllers tend to send much higher log volumes (higher EPS) than other systems, assuming they are sending all logs.
  • Database indices built on logs for efficient searching consumes significant storage as well.
  • ASCII text (syslog) compresses much better than binary (for example, Netflow)

Therefore, it is difficult to properly assume a specific bytes/log mix in your environment without measurement. Our experience from sampling of 5 large customers has shown that Bytes/log is between 100-150 including all factors – device mix, log mix, indexing cost and compression. Fortinet calculated this by dividing the total FortiSIEM event file size (in \data) over one day by the total number of events on that day, and then averaging over a few days.

It is important to provision the NFS server with enough IOPS and network bandwidth for read and write of event data and where possible cater for peaks in EPS. It is recommended that NFS is provisioned with 10Gbit interfaces or higher and the FortiSIEM Supervisor and Worker nodes to also be provisioned with 10Gbit interfaces to the NFS storage network.

The table below shows two scenarios – Worst case and average case for NFS storage. In worst case, Peak EPS and 150 Bytes/log is used. In the average case, 0.5 Peak EPS and 100 Bytes/log is used.

Peak EPS

Storage (Months)

NFS Storage (TB)*

Worst Case Average Case
1000 12 5 1.66
1000 24 9 3
1000 36 14 4.66
2000 12 9 3
2000 24 19 6.33
2000 36 28 9.33
5000 12 23 7.66
5000 24 47 15.66
5000 36 70 23.33
10000 12 47 15.66
10000 24 93 31
10000 36 140 46.66

NFS Storage (TB):

  • Worst case = (Peak EPS*150*86400*30*Storage(Months))/10^12
  • Average case = (0.5*Peak EPS*100*86400*30*Storage(Months))/10^12

Elasticsearch Based Deployment

This section provides information about the following Elasticsearch based deployment topics:

Background

An Elasticsearch deployment consists of

  • Master node (required)

  • Coordinator Only nodes (required)

  • Data nodes – Hot, Warm and Frozen (See below)

Keep the following points in mind about Hot, Warm and Frozen Data nodes:

  • FortiSIEM inserts events into Hot nodes, so Hot nodes need fast disk I/O to handle inserts and reads. A solid state drive (SSD) with more than 200Gb/s I/O throughput are recommended for hot nodes.

  • User can specify Hot node retention policy (days) in FortiSIEM. When this limit is reached, or Hot node disk usage reaches its high watermark (75% full), events are moved from Hot nodes to Warm nodes, to make room for new events in the Hot node. Warm nodes only handle event reads, so they can afford slightly lower speed disks than Hot nodes. Hard disk drives or DAS/SAN disks with about 100 Gb/s I/O throughput are recommended. Warm nodes will have similar query response times as Hot nodes, as they aren’t performing expensive indexing operations.

  • User can specify Warm node retention policy (days) in FortiSIEM. When this limit is reached, or Warm node disk usage reaches its high watermark (75% full), events are moved from Warm nodes to Frozen nodes. In the Frozen nodes, indices are flushed from memory to disk, so Frozen nodes can have much larger disks. Fortinet recommends Frozen nodes to have similar disk speeds as Warm nodes, but with larger capacity. When a user queries for data in Frozen nodes, the Frozen nodes will temporarily rehydrate the required indices to memory, and then flush to disk after the query is complete. Therefore, Frozen nodes will have higher query response time.

When using Elasticsearch in FortiSIEM, hot nodes are the minimum requirement. A budget friendly way to add additional storage is to add Warm nodes. For even more capacity, Frozen nodes can be added.

While Elasticsearch Frozen nodes can provide some Archive options, FortiSIEM provides two additional Archive options with higher compression – FortiSIEM EventDB on NFS and HDFS. Should you choose to use archiving, ensure you use the Real Time Archive option so that events are written to the Archive at the point of insertion into Hot nodes. This eliminates the need for moving data from Online to Archive, as it is prohibitively expensive to read events out of Elasticsearch and write back to Archive.

To summarize, the following options are available for Elasticsearch:

  • Online

    • Elasticsearch

      • Hot node only

      • Hot node and Warm node

      • Hot node, Warm node, and Frozen node

  • Archive

    • EventDB on NFS

    • HDFS

FortiSIEM has a dynamic shard management feature to keep Elasticsearch working optimally.

  • For Hot nodes, FortiSIEM lets a shard grow up to 40GB (Elasticsearch limit 50GB), and closes it once the 40GB limit is reached. In a low EPS situation, a shard can span multiple days. FortiSIEM uses an aliasing technique to string the shards together. In a high EPS situation, there can be multiple shards in a day.

  • Segment merge is performed to reduce heap usage for indices older than 2 days.

Recommended Elasticsearch Configuration

Fortinet recommends the following configuration steps.

  • Replica – at least 1

  • Master, Coordinator Only nodes and Data nodes on different machines

  • 3 Master nodes – each with 8 vCPU, 16 GB RAM

  • At least 2 Coordinator Only nodes – each with 16 vCPU, 32 GB RAM. Two Coordinator Only nodes are chosen for failover. The exact number of Coordinator Only nodes depends on the EPS. See below for details.

  • At least 3 Hot Data nodes – each with 32 vCPU, 64GB RAM and SSD disks with at least 200 Gb/s I/O throughput. The exact number of Hot Data nodes depends on the EPS and retention policy (see below).

  • If you decide to deploy Warm nodes, deploy at least 3 Warm Data nodes – each with 32 vCPU, 64GB RAM and disks with at least 100 Gb/s I/O throughput. The exact number of Warm Data nodes depends on retention policy (see below).

  • If you decide to deploy Frozen nodes, deploy at least 3 Frozen Data nodes – each with 16 vCPU, 64GB RAM and around 100 Gb/s I/O throughput. The exact number of Frozen Data nodes depends on retention policy (see below).

  • If you decide to utilize the Archive option, then choose the Real Time Archive option.

  • Enable FortiSIEM dynamic shard management feature (Under Shard Allocation, select Dynamic).

  • Do not choose Per Org Index unless you have to. Keeping a separate index per organization enables you to efficiently delete an organization’s data, but increases the shard count, which in turn requires more nodes because of the 500 shards per node limit.

  • Follow the Pre-install considerations in the setup guide.

Sizing of Coordinator Only Nodes

Our testing has shown that 1 Coordinator Only node with 16 vCPU and 64 GB RAM (32 GB to Elasticsearch and the rest to the operating system) can handle 200K EPS. So choose the number of Coordinator Only nodes based on your EPS and keep one extra in case a Coordinator Only node dies.

Peak EPS Coordinator Only Nodes (16 vCPU and 64 GB RAM)
50K 2
100K 2
200K 3
500K 4
1 Million 6

Sizing of Hot Data Nodes

Choose each Hot Data node to have 32 vCPU, 64GB RAM (32 GB to Elasticsearch and the rest to the operating system), and SSD with at least 200Gbps I/O throughput. Use the calculations below to find the exact number of Hot nodes. This depends on the EPS and the retention policy.

Assumptions
  • Our experiments have shown that FortiSIEM can insert 60K EPS per Data node without Replica and without any loss

  • Measurements from various SIEM installs have shown that Elasticsearch consumes an average of 500 bytes to store an event and all its parsed attributes

  • Memory to Disk Ratio = 1:30. See the Elasticsearch reference documents in References.

  • Max 75% disk capacity for storing event indices since Elasticsearch will use the rest of the 25%. See the Elasticsearch reference documents in References.

Storage per Day

Suppose

  • R: Number of Replica (at least 1 is recommended)

  • E: EPS

  • D: Retention (days) in Hot nodes

Data per day = E * #seconds in a day (86400) * 500 Bytes * (R +1)

Storage per day = 1.25 * Data per day

# Hot Data Nodes from Elasticsearch Constraint

Min # Hot Data nodes = Storage per day * D / RAM / 30

# Hot Data Nodes from EPS Constraint

Suppose

  • R: Number of Replica (at least 1 is recommended)

  • E: EPS

Since FortiSIEM can insert 60K EPS without Replica and without any loss,

Min # Hot Data nodes = E * (R+1) / 60K

Cluster Wide Shard Count Limit

In Elasticsearch 6.x, Fortinet has observed that Elasticsearch CLI performance degrades when the total number of shards in the cluster (including Hot and Warm nodes) is more than 15K. Newer versions may have a higher upper limit.

You can calculate the number of shards as follows.

  • Node Count: N

  • Disk Size on each node: D TB

Assuming 40GB per shard, the total number of shards = (N * D TB) / 40GB

For example, at 50K EPS: (consult the two tables below)

  • Hot Node: 7 days retention, number of shards = (19*2TB) / 40GB = 950

  • Warm Node: 30 days retention, number of shards = (15*10TB) / 40GB = 3750

  • Total shards in the cluster = 4700

As you map out higher EPS and longer days, make sure the total number of shards stays within the limit.

Examples

Here are some representative numbers for Replica = 1

EPS Storage per Day Retention (Days) Hot Data Nodes
(32vCPU, 64GB RAM, SSD)

Node Count Disk Size
10K 1TB 7 4 2TB
30 16 2TB
50K 5TB 7 19 2TB
14 38 2TB
30 80 2TB
100K 10TB 7 38 2TB
14 76 2TB
30 160 2TB
200K 20TB 7 76 2TB
14 152 2TB
500K 50TB 7 190 2TB
14 380 2TB
1 Million 100TB 7 380 2TB
14 760 2TB

Sizing of Warm Data Nodes

Warm nodes are configured identically as Hot Data nodes, except that memory to disk ratio = 1:160. Make sure you have 32vCPU, 64GB RAM to host with 32 GB to Elasticsearch and 32GB to the operating system. See the Elasticsearch reference documents in References.

Min # Warm Data nodes = Storage per day * D / RAM / 160

Examples

Here are some representative numbers for Replica = 1

EPS Storage per Day Retention (Days) Warm Data Nodes
(32vCPU, 64GB RAM and ~100Gbps Disk I/O)
Node Count Disk Size
10K 1TB 30 3 10TB
60 6 10TB
90 9 10TB
50K 5TB 30 15 10TB
60 30 10TB
90 45 10TB
100K 10TB 30 30 10TB
60 60 10TB
200K 20TB 30 60 10TB
60 120 10TB
500K 50TB 30 150 10TB
60 300 10TB
1 Million 100TB 30 300 10TB
60 600 10TB

Sizing of Frozen Data Nodes

Frozen nodes are configured identically as Warm or Hot Data nodes, except for a higher memory to disk ratio = 1:1000. Note that the required query latency, rather than system resources, often limits the amount of data stored on Frozen nodes. See the Elasticsearch reference documents in References.

Frozen nodes behave identically except for memory to disk ratio = 1:1000

Min # Frozen Data nodes = Storage per day * D / RAM / 1000

Examples

Here are some representative numbers for Replica = 1

EPS Storage per Day Retention (Days) Frozen Data Nodes
(16vCPU, 64GB RAM, HDD <100Gbps)

Node Count Disk Size
10K 1TB 90 2 60TB
180 4 60TB

365 7 60TB
50K 5TB 90 8 60TB
180 16 60TB
365 32 60TB
100K 10TB 90 15 60TB
180 30 60TB

365 60 60TB
200K 20TB 90 30 60TB
180 60 60TB

365 120 60TB
500K 50TB 90 75 60TB
180 150 60TB
365 300 60TB
1 Million 100TB 90 150 60TB
180 300 60TB
365 600 60TB

ClickHouse Based Deployment

Processing Requirement

EPS

Nodes

HW per Node (vCPU, RAM)

Disk Type

Up to 5K All-in-one 16, 24GB 2 tier (SSD,SAS) with RAID recommended but not required - see FSM-2000G hardware spec. If you use one tier then SAS disks are preferred.
5K - 10K All-in-one 24, 32GB 2 tier (SSD,SAS) with RAID recommended but not required - see FSM-2000G hardware spec. If you use one tier then SAS disks are preferred.
10K - 15K All-in-one 32, 48GB 2 tier (SSD,SAS) with RAID recommended but not required - see FSM-2000G hardware spec. If you use one tier then SAS disks are preferred.
15K - 40K All-in-one 48, 64GB 2 tier (SSD,SAS) with RAID required - see FSM-2000G hardware spec

See ClickHouse Usage Recommendations in References for more information.

Storage Requirement for ClickHouse

ClickHouse Storage requirement is the same as FortiSIEM EventDB. Consult that section for calculating storage sizes for your environment. If you choose 2 tier storage, then the size of the SSD can be chosen based on budget and number of days for which very fast query response is required.

Sizing Archive Deployments

FortiSIEM Event Archives can be based on FortiSIEM EventDB on NFS or HDFS.

FortiSIEM EventDB Based Deployments

In this situation, online workers are used to query the Archived EventDB database, so only a NFS infrastructure is required. Since Archived data is not indexed, our experiments have shown that Archived EventDB needs about 60% storage compared to Online EventDB. This information can be used to estimate the amount of NFS storage required for Archive.

EPS Retention NFS Storage
Worst Case (100 Bytes/log) Average Case (66 Bytes/log)
5K 6 months 7.5 TB 2.5 TB
1 year 15 TB 5 TB
3 years 45 TB 15 TB
10K 6 months 15 TB 5 TB
1 year 30 TB 10 TB
3 years 90 TB 30 TB
20K 6 months 30 TB 10 TB
1 year 60 TB 20 TB
3 years 180 TB 60 TB
50K 6 months 75 TB 25 TB
1 year 150 TB 50 TB
3 years 450 TB 150 TB
100K 6 months 150 TB 50 TB
1 year 300 TB 100 TB

3 years 900 TB 100 TB

Worst Case Storage = EPS * 86400 * worst case bytes/log * retention

Average Case Storage = 0.5* EPS * 86400 * average case bytes/log * retention

Used 1024 for B -> KB etc.

HDFS Based Deployments

An HDFS based deployment needs the following:

  • Name node

  • Spark Master node

  • Spark Slave node

  • Data node

According to HDFS best practices, the following co-locations are possible:

  • Node Type A containing Name node – need 2 of these – 8vCPU and 16GB RAM each

  • Node Type B containing Spark Master and Slave node – need 2 of these - – 8vCPU and 16GB RAM each

  • Node Type C containing Slave node and Data node – need N of these based on insert and query requirements.

Our experiments have shown that

  • HDFS Parquet file system uses 125 bytes/event (25% of Elasticsearch storage and 30% more than FortiSIEM EventDB).

  • HDFS can insert events at 200K EPS per Data node, so insert speed is not a determining criteria.

Spark / HDFS Resource Allocation Considerations

Spark / HDFS can run the following 4 jobs.

  1. Real time Archive job

  2. Non-real time Archive job

  3. Query Job from Supervisor

  4. Merge job to merge small files written to HDFS into bigger files

The resource allocation strategy is as follows:

totalCore = Total number of cores on Spark Worker nodes

totalWorker = Total number of Spark Worker nodes

availCore = (totalCore-totalWorker) available to the 4 job types above

nodeCore = Total number of cores on one single Spark worker node

Strategy
  1. Real time archive job is allocated rm_lambda_percent (default 30) of resources. This parameter is defined in /home/admin/FortiSIEM/config.txt.

  2. Remaining resources are allocated to 3 other job types in an equal manner. The parameter rm_max_concurrent_jobs (default 5) defined in /home/admin/FortiSIEM/config.txt defines the maximum number of such jobs. Each executor needs to be allocated 5 cores to run, Hence the maximum value of rm_max_concurrent_jobs should be the minimum value of the following two calculations:

    1. (availCore * ((100 - rm_lambda_percent) / 100)) / 5.

    2. (nodeCore - 1) * ((100 - rm_lambda_percent) / 100) / 5 * totalWorker

These two calculations may differ as the lower integer needs to be retrieved when dividing by 5.

Example

10 Spark nodes each 16 core and 32GB RAM.

totalCore = 160

totalWorker = 10

availCore = 150

rm_lambda_percent = 30

rm_max_concurrent_job = 20

  1. Real time archive job will be assigned with at most 9 executors, each with 5 core and 10GB RAM. Spark will dynamically adjust the executor numbers based on running status.

  2. A resource pool of 20 jobs are created, each with 5 core and 10GB RAM. Each of these can run the other 3 jobs based on demand.


Based on this, the following sizing is suggested.

EPS

Storage per Day

(Replica = 1)

Retention

Total Storage

Spark Slave + Data Node

(16 vCPU, 32GB RAM, HDD – 100 Gbps)

Count Disk Storage
10K 125 GB 1 year 45 TB 6 8 TB
3 years 134 TB 6 24 TB
50K 625 GB 1 year 225 TB 10 24 TB
3 years 675 TB 10 80 TB
100K 1.25 TB 1 year 460 TB 10 48 TB
3 years 1,380 TB 10 160 TB
200K 2.5 TB 1 year 920 TB 10 96 TB
3 years 2,760 TB 10 300 TB
500K 5.75 TB 1 year 2,250 TB 8 300 TB
3 years 6,750 TB 25 300 TB
1 Million 11.5 TB 1 year 4,450 TB 15 300 TB
3 years 13,350 TB 25 600 TB

References

Elasticsearch Concepts and Sizing Guide

https://www.elastic.co/pdf/elasticsearch-sizing-and-capacity-planning.pdf

Elasticsearch Sizing Guide

https://www.elastic.co/blog/benchmarking-and-sizing-your-elasticsearch-cluster-for-logs-and-metrics

ClickHouse Usage Recommendations

https://clickhouse.com/docs/en/operations/tips/